Am I being thick? Why would you want to silence a fire alarm sounder in a flat?

devices in flat controlled by push to hush, gives the occupier the chance to control local false alarm before full building goes into evac

Mr th2.jpg Veritas God

Link to comment
Share on other sites

I see, it's like a suppression so that you can investigate the reason for the trigger in your own flat before having everyone out.

Burnt toast.

Personally I refuse to fit them.

But HMO`s do have them as standard now.

I thought it hushed a fire alarm already in evac, that's what I couldn't understand.

www.securitywarehouse.co.uk/catalog/

Link to comment
Share on other sites

I see, it's like a suppression so that you can investigate the reason for the trigger in your own flat before having everyone out.

I thought it hushed a fire alarm already in evac, that's what I couldn't understand.

Nah, stops a full evac on burnt toast.

C-Tec is a nice panel (The addressable one) this thing drags it down.

Better than that Aico stuff though!!!

Link to comment
Share on other sites

I thought it hushed a fire alarm already in evac, that's what I couldn't understand.

The Hush button takes two address spaces on the main panel (one for detection, one for sounder).

Detection/sounders connected to the button are conventional.

If these are triggered only the sounders connected to the local hush button sound.

If the smoke clears the hush button silences the alarm, if not the hush button triggers the addressable zone.

This evac's the whole building or multiple panels if networked.

Link to comment
Share on other sites