December 16, 201015 yr comment_262355 Also how long has this been fitted? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262355 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 16, 201015 yr comment_262356 I would replace net 1 expander 5 The opinions I express are mine and are usually correct! (Except when I'm wrong)(which I'm not) Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262356 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 16, 201015 yr comment_262357 are you running this expander 70m on normal cable? and there is still 12.7v at the expander? Seems like voltage / line length to me. Can you double / treble up the supply cables? tbh i can't see why he isn't powering the expander from the PSU? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262357 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 16, 201015 yr comment_262358 are the expanders powered by local power supplpies, or is the psu by the panel? securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262358 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 16, 201015 yr comment_262360 I have reconnected the network cables to the panel today and made sure that the power supplies only power detectors and not expanders, they will be powered directly from panel so we will see tonight. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262360 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 16, 201015 yr comment_262362 Whats the Voltage at the expander end? IMHO this is the most important question, I reckon there borderline during the day & the falling temp is marking the current consumption increase ? Mr Veritas God Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262362 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 17, 201015 yr Author comment_262438 good morning. The power supply is at the expander, 1 for each expander. I am running 0,5mm cable for network only. Software shows voltage as reported. Using 4 core 0,5mm cable. Have replaced expander 5 and keypad powered from it. Have a grea day out there all. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262438 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 17, 201015 yr Author comment_262444 hi again. problem seems to be resolved. found this morning that there is a master switch that some person wired that would normally turn of only the lights but in stead turns of all power, including dedicated power circuit, in the new section of the basement.this has never been a problem before, but the cleint had removed the computers from this area, and had it rewired. thanks to ignorance and lack of input this problem lasted this long. thanks for all the input every body, just sorry I had to waste everybody's time, including my own. have a fantastic season. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262444 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 17, 201015 yr comment_262447 hi again. problem seems to be resolved. found this morning that there is a master switch that some person wired that would normally turn of only the lights but in stead turns of all power, including dedicated power circuit, in the new section of the basement.this has never been a problem before, but the cleint had removed the computers from this area, and had it rewired. thanks to ignorance and lack of input this problem lasted this long. thanks for all the input every body, just sorry I had to waste everybody's time, including my own. have a fantastic season. Main thing is you've resolved the 'fault'-just a case of how much you're going to charge them now!.......Seasons greetings, for the update Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262447 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
December 17, 201015 yr comment_262452 I was right then #2 That's rare Lol securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/30444-texecom-168-network-problem/page/2/#findComment-262452 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post