Your question isnt clear but I guess you are asking about connecting the fire alarm to the access control to release the doors when the fire alarm goes off.
To be compliant you should wire them in series with the locks not into the controller, they should in the event of a fire drop the power to the lock as default. If you wire them to an input on the Paxton and programming the paxton to release the doors, then you are reliant on the Paxton kit working when a fire breaks out which then means the Paxton has to be compliant to BS5839 which its not
  • Upvote 1
On 31/03/2023 at 18:00, David Walsh said:
Thank you. What do you mean locks not in the controller?
As a newbie or chancer as some might say
I assuming you need to fit something in-between the lock and the controller , this way controller has no choice that doors are released ???
Al drop the chancher bit, your asking, if you cant ask with some positive feedback tsi is dead.
As Pete says the fire overide needs to be at each head droping the power to each lock as part of the fire not a network intruction
I was handed mine earier today as functional earths need a different colour I need to get back in the ring
It's usually down to who controls what tho.
Who will commission the fire etc.
I would always expect one for one unless told and confirmed in writing otherwise.
You want to minimise the length of the runs from the fire system and also minimise failures if there is an issue with the loop.