martinhendo Posted December 7, 2022 Share Posted December 7, 2022 First ever post on here.. Been in and around the F&S installation game for a few years now but have never come across this, maybe one of you guys could shine some light on it. New installation of a 264, Line 1 has 2 x C072's and 1 x P026, no RKP or other modules on the bus, everything is programmed and tested on this line. Line 2 has 5 x C072's and 2 x P026's, along with 1 CP037 RKP and MX4 Prox. Rio's are addressed from 201 > 207, all devices on Rios 201 > 206 have been tested with no issues, RKP and Prox reader function as expected On to the issue, Rio 207 (Furthest away from main panel, power sourced from Rio 205, 23m distance, 680 resistor fitted and link removed in panel) 13.8 v @ Rio 207. On carrying out a walk test on each zone individually, Z2073 a DT along with Z2077 a DC gave no response to the walk test. The other 6 zones had no issues. The zone resistances of Z2073/Z2077 via option 21, 1K ohms when closed, and when resistance rises to 1K9 (roughly) the panel still returns a closed message, all zones are set to default EOL. Replaced DT and DC, and tested cables from them @ the Rio, 1k closed, 1K9 Open (roughly) on each. Tested the cable from the detection end while connected to Rio, shows S/C on panel around 12 Ohms resistance. Swapped the Rio for another that's known to work and the same issue remained.. Honeywell may be getting a call when I am back @ site.. Your input would be appreciated.. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/ Share on other sites More sharing options...
al-yeti Posted December 7, 2022 Share Posted December 7, 2022 41 minutes ago, martinhendo said: First ever post on here.. Been in and around the F&S installation game for a few years now but have never come across this, maybe one of you guys could shine some light on it. New installation of a 264, Line 1 has 2 x C072's and 1 x P026, no RKP or other modules on the bus, everything is programmed and tested on this line. Line 2 has 5 x C072's and 2 x P026's, along with 1 CP037 RKP and MX4 Prox. Rio's are addressed from 201 > 207, all devices on Rios 201 > 206 have been tested with no issues, RKP and Prox reader function as expected On to the issue, Rio 207 (Furthest away from main panel, power sourced from Rio 205, 23m distance, 680 resistor fitted and link removed in panel) 13.8 v @ Rio 207. On carrying out a walk test on each zone individually, Z2073 a DT along with Z2077 a DC gave no response to the walk test. The other 6 zones had no issues. The zone resistances of Z2073/Z2077 via option 21, 1K ohms when closed, and when resistance rises to 1K9 (roughly) the panel still returns a closed message, all zones are set to default EOL. Replaced DT and DC, and tested cables from them @ the Rio, 1k closed, 1K9 Open (roughly) on each. Tested the cable from the detection end while connected to Rio, shows S/C on panel around 12 Ohms resistance. Swapped the Rio for another that's known to work and the same issue remained.. Honeywell may be getting a call when I am back @ site.. Your input would be appreciated.. What happens if you add another Rio on the end ? Programme it in Sounds like job for jw or gg or some dude in err can't remember rich? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517251 Share on other sites More sharing options...
martinhendo Posted December 7, 2022 Author Share Posted December 7, 2022 Haven't tried adding anything onto the existing bus line due to time restraints today Everything looks from the outside, comm's 100% with all Rio's on both lines.. Lines are run in belden. Just haven't come across something as weird as this. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517252 Share on other sites More sharing options...
sixwheeledbeast Posted December 7, 2022 Share Posted December 7, 2022 I am no Galaxy expert but have you done any tests on the bus? I have known people to remove the termination to solve some issues. Is there a ground loop? Resite the RIO adjacent to the downstream one on a metre of cable? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517253 Share on other sites More sharing options...
james.wilson Posted December 8, 2022 Share Posted December 8, 2022 are you sure the resistor values are default on the affected circuits. if the panel is showin a 2k resistance but showing closed looks like programming to me securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517257 Share on other sites More sharing options...
martinhendo Posted December 8, 2022 Author Share Posted December 8, 2022 4 hours ago, james.wilson said: are you sure the resistor values are default on the affected circuits. if the panel is showin a 2k resistance but showing closed looks like programming to me Panel and all Rio's are set to system default, 1K balanced/eol, Having already checked that. Zones 2071 > 2072, 2074 > 2076 and 2078 are all working as expected with exactly the same resistor setup. The 2 zones are also on separate locations. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517259 Share on other sites More sharing options...
martinhendo Posted December 8, 2022 Author Share Posted December 8, 2022 8 hours ago, sixwheeledbeast said: I am no Galaxy expert but have you done any tests on the bus? I have known people to remove the termination to solve some issues. Is there a ground loop? Resite the RIO adjacent to the downstream one on a metre of cable? Haven't looked @ the bus as of yet, not had time. Might give it a shot when back on site, worth a crack. Thanks.. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517260 Share on other sites More sharing options...
james.wilson Posted December 8, 2022 Share Posted December 8, 2022 2 hours ago, martinhendo said: Panel and all Rio's are set to system default, 1K balanced/eol, Having already checked that. Zones 2071 > 2072, 2074 > 2076 and 2078 are all working as expected with exactly the same resistor setup. The 2 zones are also on separate locations. ok id leave the rio where it is and disconnect all the circuits at the rio end and link all circuits with a 1k resistor. Then assuming all show 1k closed change each circuit to 2k one at a time. What do you get then? Is all detection cabling new? securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517261 Share on other sites More sharing options...
martinhendo Posted December 8, 2022 Author Share Posted December 8, 2022 New install.. Found out what the problem was, one of the jumpers on the RIO wasn't making a true connection, replaced both jumpers, power cycled and 2 hours ago, james.wilson said: ok id leave the rio where it is and disconnect all the circuits at the rio end and link all circuits with a 1k resistor. Then assuming all show 1k closed change each circuit to 2k one at a time. What do you get then? Is all detection cabling new? New install.. Found out what the problem was, one of the jumpers Slave/EE on the RIO wasn't making a true connection, replaced both jumpers, power cycled and problem sorted. Really strange, haven't seen that happen before. Every day certainly is a school day. Thanks for the replies.. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517262 Share on other sites More sharing options...
sixwheeledbeast Posted December 8, 2022 Share Posted December 8, 2022 16 hours ago, martinhendo said: Swapped the Rio for another that's known to work and the same issue remained. I thought you had swapped the RIO? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/45415-dimension-264-strange-issue/#findComment-517263 Share on other sites More sharing options...