First ever post on here..
Been in and around the F&S installation game for a few years now but have never come across this, maybe one of you guys could shine some light on it.
New installation of a 264, Line 1 has 2 x C072's and 1 x P026, no RKP or other modules on the bus, everything is programmed and tested on this line.
Line 2 has 5 x C072's and 2 x P026's, along with 1 CP037 RKP and MX4 Prox.
Rio's are addressed from 201 > 207, all devices on Rios 201 > 206 have been tested with no issues, RKP and Prox reader function as expected
On to the issue, Rio 207 (Furthest away from main panel, power sourced from Rio 205, 23m distance, 680 resistor fitted and link removed in panel) 13.8 v @ Rio 207.
On carrying out a walk test on each zone individually, Z2073 a DT along with Z2077 a DC gave no response to the walk test.
The other 6 zones had no issues.
The zone resistances of Z2073/Z2077 via option 21, 1K ohms when closed, and when resistance rises to 1K9 (roughly) the panel still returns a closed message, all zones are set to default EOL.
Replaced DT and DC, and tested cables from them @ the Rio, 1k closed, 1K9 Open (roughly) on each. Tested the cable from the detection end while connected to Rio, shows S/C on panel around 12 Ohms resistance.
Swapped the Rio for another that's known to work and the same issue remained..
Honeywell may be getting a call when I am back @ site..
Your input would be appreciated..