Don't forget you need headroom to recharge the battery after a mains fail and consider standby time. 

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Oh ok 240 is fine I wouldn't personally go above 75 percent on alarm so I'd either put a psu in or scb more sounders

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Thanks, worst case i will scb both external sounders, do you think it would work in reality? The elm300 i intend add will draw 80ma max but i imagine once its onboard batteries are fully charged it will be even less than that. Did you ever use these panels? If so can you remember what the hold off circuit is rated at?

Cheers 

5 hours ago, CR Alarms said:

Thanks, worst case i will scb both external sounders, do you think it would work in reality? The elm300 i intend add will draw 80ma max but i imagine once its onboard batteries are fully charged it will be even less than that. Did you ever use these panels? If so can you remember what the hold off circuit is rated at?

Cheers 

SCB both , no one listens to them outside much 

 

Your better off making sure internal Sounders are adequate and signalling 

You do have a point tbh, i rarely see anyone take any notice of a bell box sounding, the internal sounder i have at the moment is the elmdene speaker which is Loud but not quite loud enough to drive you out house hence why i bought the elm300 give the sound a boost indoors.

Just one more thing regarding the panel power supply, does each 12v output such as the bell circuit have its own individual polyswitch?, if so what are they rated at? Or are all the 12v outputs commoned together and protected by one big polyfuse rated at 1250ma at 20 degrees and at worst case 800ma at 40 degrees?

Cheers 

3 minutes ago, Logan said:

Yes   im well familiar with the 9600   strange panel as the 9800 came out later with 2 7 segment led displays like the 9100 ,which is scantronics first panel 

Launched because the market demanded a lower cost

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.