Hi, I installed a hardwired challenger alarm system in a domestic property and the system included an auto voice dialler.
The entire system works fine except from the auto dialler.. It doesnt call the programmed phone numbers when the alarm is triggered, but as soon as you enter the user code to turn the alarm off it starts ringing..
also if you remove the cover from the autodialler to release the tamper spring it makes the call but does not trigger the alarm.

Any ideas what this could be?
Checked all connections and they are as shown on the wiring diagram
 
The auto dialler is a separate unit from the main panel
 
Autodialler is the AT60
Main panel is the AP10LED
3 hours ago, sixwheeledbeast said:

Output or input needs inverting if it's doing the opposite.

Also tamper connections not connected to the panel?

 

Tamper connections run from autodialler to panel and are functioning, why would the output need inverting if its connected as stated on wiring diagram? (genuine question)

 

 

Things generally don't just work by sticking wires in holes with security systems, they still need programming for the use case.

More complicated the panel or configuration the more complicated the programming gets.

49 minutes ago, ChrisH1 said:

 

Tamper connections run from autodialler to panel and are functioning, why would the output need inverting if its connected as stated on wiring diagram? (genuine question)

 

Do CEF get them from tomy or fisher price?

 

challenger_at60_b_d5c071827c1d942e3c22d1

Mr th2.jpg Veritas God

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.