  1. Today
  2. You are not reading what he typed correctly he typed "with the panel and sensors pulling 0.55 A" Now there was no mention of mA so 0.55A no matter how you try to dress that up is slightly over half an amp. He may have made a mistake but either way what he typed is 0.55A not 0.055A which would be 55mA
  3. Yesterday
  4. Theres 1000 mA to an amp not 100 550mA would be half an amp (well over half an amp)
  5. So I'm thinking this low measurement could be due to voltage drop on the connecting leads (which could amount to a few tenths of a volt at that current). The panel will only measure voltage at the board during a load test.. Next step is to check voltage at the actual terminals of the battery.
  6. if the float charge is only 22 mA, it could take more than 24 to fully charge the battery, depending on its initial charge state. It is a 7 Ah battery.
  7. I've got 5 PIRs (older ones so current consumption might be higher than newer ones). Also 6 shock sensors, a wired bell and two wired keypads. That's 14 devices (and there's also the panel itself that has to be powered), so if they're pulled a few tens of milliamps, it could add up. I'd have to check all the specs to see what the current consumption is.
  8. So I left it for 3 days and performed a longer test this time. After ten minutes pulling 0.55 A, voltage stabilised at 11.9 V. (it was at 11.9 V after around 2 minutes).
  9. Last week
  10. It should recharge within 24 hours. Also needs to, to comply
  11. Yep I'd also assume the PIR's are in Auto and sleeping. Door contacts shouldn't do that unless you have programmed them incorrectly. They default to always awake.
  12. Two things of note here, if your panel is pulling over half an amp quiescent that seems quite high to me and also if your new battery is dropping to 12v under load I would suggest its not a good battery.
  13. Most likely because you are activating the devices just before or during the setting procedure. Wireless devices will go to sleep for a short period after activation to conserve battery life. If you try triggering a device that has not activated recently you should find the system will respond almost immediately.
  14. I'll see if I can find some charge/discharge curves. Presumably if the battery was sitting on a shelf in a store, it may have self-discharged somewhat. Not sure what the self-discharge rate is for lead acid, but 12.9 V would have indicated that it was fully charged, but maybe not. I guess there's some variability. The panel is trickle charging it at 22 mA. That figure was 38 mA for the 6 year old battery (which I thought was a Yuasa, but it was an Interlogix. I presume these are just badged and there are a limited number of battery manufacturers)
  15. I’m after putting a new 12 V, 7 AH lead acid battery into my alarm panel. Off load voltage was 12.9 V at the battery terminals before fitting. A fully charged 12 V battery should read around 12.8 V. When I did a load test, with the panel and sensors pulling 0.55 A, the voltage eventually dropped to 12.0 V before I stopped the test after a few minutes (the voltage fell faster at first). Float charge voltage for a lead acid battery (and from a panel) is typically 13.8 V. So just wondering since the battery isn't charged in a three state mode by a panel like a normal charger would charge it (constant current, constant voltage and then trickle maintenance charge), how long typically does it take a new battery to fully charge? I've seen figures of 24 to 48 hours mentioned.
  16. Ive installed my self but it takes ages before it sets of the alarm and thats me walking by all the IR Beams and door contacts Does anyone know the most likely reason for the lengthy delay before the alarm sounds? maybe 1-3 minutes not timed it yet
  17. Its unlikely anyone here would know it was a primarily DIY product, my best guess would be to change the wireless codes, very early wireless stuff allowed you to set codes so that it did not interfere with neighbours alarms and vica versa
  18. Does anyone know what the switch pack on a infinite prime motherboard is for please
  19. cqr used to have clear plastic & you could see them inside I use to find them inside cables upto 1m or so, I reckon they crawled in, & each time one crawled in behind the they;d move up more ? battery in sounder will last 2yrs or 20 yrs....
  20. Battery not at fault, it was the piezo element. However HKC say the battery should be good for 5 years, and now it's 8 years. However I tested it, and it can still power the sounder for the 15 mins set by the jumper.
  21. I thought something like that may have caused it. Blew the plastic horn out with an air compressor, but it didn't make any difference. There was some corrosion around where the leads were soldered onto the element (it's just a flat disc with a metal plate on one side and a metal coating on the other). Cleaning that didn't do anything either. So I reckon the crystal just cracks and can't vibrate properly.
  22. pizeo's vibrate, thrips / thunder bugs or whatever climb inside stuff & don;t vibrate no more...
  23. That's the one I salvaged the piezo element from, which is working fine now in the HKC one. So does anyone know whether 120 V AC is a standard voltage for these?
  24. Didn't realise it was old bell , bin it now
  25. 120 V AC. Presumably that's RMS , because peak voltage is nearly 250 to 300 V. This is the waveform on a scope. Anyway I had a stroke of luck. My old sounder has the exact same piezo transducer so I'm going to use that. Hopefully it's the same voltage, but it looks totally identical. The HKC sounder is taking nearly 200 mA when sounding after I replaced the piezo element, which tallies with the 250 mA peak they give in the spec. Also the 6 V battery is still working fine. After 15 mins of alarming, voltage fell to 5.75 V.
  • Who's Online   0 Members, 0 Anonymous, 69 Guests (See full list)
    52,016
    riccardo
    riccardo
    446.3k