June 1, 200520 yr comment_55487 I've been installing an Accenta G3 mini and got it all working (quite pleased with myself However, the manual recommends a dedicated spur to the main fuse board... 1) I don't have and spare breakers on my main fuse board, and 2) It would be extreemly difficult to get a spur back to the board. Is it 'ok' to take a spur off a socket loop? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55493 Yes, install a fused spur using the same size twin and earth as the socket you are spuring of (i.e. 2.5mm2, and fit it with a 3amp fuse. The fused spur should be adjacent to or next to the alarm control panel. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55493 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55505 Don't forget it should be an unswitched FCU. Trade Member Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55505 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55506 And try to make sure that this circuit isn't on an RCD (earth leakage device) as a lot of socket circuits are and this may lead to nuisance tripping of the supply to the alarm panel........... not a good idea. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55506 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55507 Good point Antinode Edited June 1, 200520 yr by DNS Security Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55507 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55526 Is this not where part 'P' kicks in? Nothing is foolproof to a sufficiently talented fool. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55526 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55527 Should do probably - But Ive heard rumours part P is going to run into trouble soon.... Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55527 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55531 Is this not where part 'P' kicks in? 55526[/snapback] As its not a new circuit or (I assume) in a kitchen or bathroom, part P (P is for P*ss take) does not apply. Fire Member Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55531 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55532 Should do probably - But Ive heard rumours part P is going to run into trouble soon.... 55527[/snapback] Hope not, I've spent a small fortune on registration. (ECA want extra dosh while NIC lads get it for nowt!!!! Fire Member Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55532 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 1, 200520 yr comment_55540 You can spur off an existing circuit, aslong as it's not in a kitchen or bathroom, as John says. You'll only have problems if you run a new circuit from the CU. How this is any more dangerous or difficult than spurring from an existing circuit I'll never know. Part P is just one big joke as far as I'm concearned, but let's not go there... Trade Member Link to comment https://www.thesecurityinstaller.co.uk/community/topic/6343-dedicated-spur/#findComment-55540 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post