luke5853 Posted September 15, 2024 Share Posted September 15, 2024 I have recently installed a new veritas r8 panel, with the remote keypad and 6 capture p15 and 2 door contacts. All PIRs illuminate when activated, door contacts work as expected. No tampers on system. When arming the system or preforming a walk test the PIRs illuminate but do not register on the keypad. Any advice would be great Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/ Share on other sites More sharing options...
MrHappy Posted September 15, 2024 Share Posted September 15, 2024 on the back of the sensor there is slide for eol vaule it needs to be n/c... Mr Veritas God Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/#findComment-525212 Share on other sites More sharing options...
luke5853 Posted September 15, 2024 Author Share Posted September 15, 2024 (edited) @MrHappy thank you. Little confused as the guide states "The device is defaulted to the Texecom EOL values. Use a terminal driver to move the switch to any other position. The O/C position can be used for other wiring types, including use of resistor values which are not included on the device Terminal block identification." Obviously both items are texecom so why would I change it to o/c. Thanks you Edited September 15, 2024 by luke5853 Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/#findComment-525213 Share on other sites More sharing options...
sixwheeledbeast Posted September 15, 2024 Share Posted September 15, 2024 The Veritas is a double pole panel so you need normally closed devices (without resistors). The Texecom setting on the Capture PIR's is for Texecom EOL circuits. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/#findComment-525214 Share on other sites More sharing options...
al-yeti Posted September 15, 2024 Share Posted September 15, 2024 4 minutes ago, luke5853 said: @MrHappy thank you. Little confused as the guide states "The device is defaulted to the Texecom EOL values. Use a terminal driver to move the switch to any other position. The O/C position can be used for other wiring types, including use of resistor values which are not included on the device Terminal block identification." Obviously both items are texecom so why would I change it to o/c. Thanks you As you set your panel non eol and pirs are eol , so you would change it Just now, sixwheeledbeast said: The Veritas is a double pole panel so you need normally closed devices (without resistors). The Texecom setting on the Capture PIR's is for Texecom EOL circuits. This is the posh answer Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/#findComment-525215 Share on other sites More sharing options...
luke5853 Posted September 16, 2024 Author Share Posted September 16, 2024 Thanks all. This resolved the issue. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/#findComment-525231 Share on other sites More sharing options...
MrHappy Posted September 16, 2024 Share Posted September 16, 2024 4 minutes ago, luke5853 said: Thanks all. This resolved the issue. I've only do this 30 odd years Mr Veritas God Link to comment https://www.thesecurityinstaller.co.uk/community/topic/46910-veritas-r8-texecom-panel/#findComment-525233 Share on other sites More sharing options...