Honeywell gen4 alarm
Hi guys
I'm an electrician by trade but been asked to try sort an alarm out at the property I'm currently working at and was hoping some one could offer abit of advice
The alarm panel is a honeywell accenta g4 and the pir's are honeywell 8IR103
When trying to set it just keeps beeping and doesn't actually set. When pressing the up arrow it gives all 8 zones in arming fault.
When trying to do a walk test all zones are already 1 rather than changing from 0 to 1.
I've factory reset the panel to default settings and still the same.
I've took zone one out and put a a link in. The arming fault disappears on zone 1 and walk test is 0 like it should.
What am I missing with the pic's? Are they compatible with the panel or is they a normally open or normally closed that needs changing?
It's like the pir's are staying open and not closing. Also the leds aren't working on the pir's even though the jumper is set to on.
Any help would be appreciated
Edited by sparks-2012
1 minute ago, sparks-2012 said:
Hi guys
Cable faults?
If you link out all the zones does that clear the LEDs?
1 hour ago, al-yeti said:
Cable faults?
On all 8 cables and only on the alarm cores? Tamper and voltage working as it should
I only linked out 1 zone as was strapped for time
If all the cables took one route then anything is possible
If it were me , Identify zone 1 and see what the equipment is at the other end
Defaulting is good , but now you need to set each zone attributes
Hence why I would link out all the zones and trace them one by one and clear each fault
And that's once I know the panel is clear of all faults
I can't remember the panel much , but I assume it was a global tamper so loop that aswell
Does the external bell work?
don't get involved in alarms is best advice I can offer...
do you have 12v dc at every pir, have you checked the fuse...
Yes external bell works find. Tamper works at pirs and yes it's a global tamper.
I try not to but the old while your here can you have a look at this. The ones pir I took down had 12v at it. I did notice in the pir there was 2 eol connections with nothing in. Is that possibly why?.
The PIR you mentioned earlier doesn't have eol are you saying model is different now?
This is the pir with model 8IR103. If you scroll down you can see a picture of the terminals
https://www.citysecuritysystems.co.uk/honeywell-8ir103-pet-security-product
Has it never worked?
Not sure. They moved in in February and hasn't worked but unsure if the previous owners had it working