19 minutes ago, bdo21 said:

Yes for the architect and electrical contractor. It came up when the electrical contractor were reviewing the plans and then confirmed with building control.

 

err..have'nt interlinked mains powered smoke alarm been a requirement for new builds for the last 25yrs or so ?

 

19 minutes ago, bdo21 said:

We don’t have any smoke alarm system currently - it is a newbuild house. We had planned nest protect - nothing sophisticated!

 

Looking at there site its does'nt appear to confirm to any std ?

 

Is the property wired & plastered yet ?

Edited by MrHappy

Mr th2.jpg Veritas God

Texecom panel does not comply to BS5839 part 6  LD2/3/4 Grade B its an intruder alarm that has the ability to take smoke detectors, but these are purely to be treated ancillaries and do not comply with BS5839 in any way  

Just now, PeterJames said:

Texecom panel does not comply to BS5839 part 6  LD2/3/4 Grade B its an intruder alarm that has the ability to take smoke detectors, but these are purely to be treated ancillaries and do not comply with BS5839 in any way  

 

Thank you for the very clear response! I clearly need a separate fire alarm and link it to the Texecom panel for notifications, etc. 

9 minutes ago, bdo21 said:

I guess nobody thought of this before then.

 

you doing  a wanky "grand design" project ?

 

I'd assume you need either need mains powered interlink smoke detectors or bs 5839 pt1 fire alarm

 

normally somebody with an understanding of construction & buildings regulations like a competent architect would have advised or taken advice on whats required ?

 

 

Mr th2.jpg Veritas God

1 minute ago, bdo21 said:

and link it to the Texecom panel for notifications, etc. 

 

Texecom connect ?

 

If the house is high end, & the requirement is for a proper fire alarm signalling via an intruder alarm isn't good eneough

Mr th2.jpg Veritas God

So "Grade B"



Grade B - Fire detection and alarm system comprising fire detectors (other than smoke alarms), fire alarm sounders and control and indicating equipment to either BS EN 54-2 (and power supply to BS EN 54-4), or to Annex C of BS 5839: Pt.6

Mains interlinked would be Grade D, so not good enough for building control due to being over 200m2. 

You need to speak to a fire alarm installer, they would be able to liaise with building control about the Grade and Category if required.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.