July 8, 201015 yr comment_244895 Premier 48 v8.25 software with Zone 1 set up as Guard Access type in Area A. Quote from manual "This zone type will also start the entry mode when the system/area is part armed and activate any output programmed as "Guard Access Alarm." Therefore when the system is part armed, my interpretation is that activating zone 1 should start the entry timer, and give me 30 seconds to type in my code and unset the system. However, activating Zone 1 when part set seems to set off an immediate intruder alarm. Is my interpretation incorrect? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 8, 201015 yr comment_244904 G attribute in attributes 1 for that zone? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244904 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 8, 201015 yr Author comment_244905 Only attributes set in 1 and 2 are Omittable and Auto Rearm. Using Wintex to set up. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244905 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 8, 201015 yr comment_244916 Premier 48 v8.25 software with Zone 1 set up as Guard Access type in Area A. Quote from manual "This zone type will also start the entry mode when the system/area is part armed and activate any output programmed as "Guard Access Alarm." Therefore when the system is part armed, my interpretation is that activating zone 1 should start the entry timer, and give me 30 seconds to type in my code and unset the system. However, activating Zone 1 when part set seems to set off an immediate intruder alarm. Is my interpretation incorrect? not into the panel so don't flme me please, should it not be 'final exit/entry' in part set (or somthing like it), not an 'access' zone which i'd view as a pass through zone on entry exit as in a passage pir? Arfur If you think education is difficult, try being stupid!!!! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244916 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 9, 201015 yr comment_244920 on the prem zone types are overwridden by attributes. Galaxy has a similar zone type for security zones that are then e/e during setting etc. Allows fire doors to be protected during the day, but used as final doors too. securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244920 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 9, 201015 yr Author comment_244922 The zone is a kitchen pir sensor, which is on the exit route. Guard Access works correctly when full arming on leaving the house, as activating the zone during the exit or entry timer does not set off the alarm. Activating the zone when the system is full armed causes an immediate alarm, which is correct. I would like to use part set in the evening, such that the downstairs internal pirs start the entry timer when activated, not cause an immediate alarm. Is it possible to do this? Thanks! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244922 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 9, 201015 yr comment_244935 again, on all the panels i've ever used, 'access' is a pass through, i.e armed when set immediate response only if the/a final door is not opened 1st. Gardtec Risco panels (which i use), has a zone type setting to make your kitchen and other PIR's act as the final door in part set i.e. 'entry/exit in part set' not plain 'access'. i'm sure someone will post the exact reference when read, many know the panel. failing that try -: Technical Support: UK Customers Tel: 08456 300 600 you might be lucky Arfur Edited July 9, 201015 yr by arfur mo If you think education is difficult, try being stupid!!!! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244935 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 9, 201015 yr comment_244937 see Page 9 of installation manual options 50, 51 and 52 select as required Arfur If you think education is difficult, try being stupid!!!! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244937 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 9, 201015 yr comment_244980 You have to give the zone the entry attribute The opinions I express are mine and are usually correct! (Except when I'm wrong)(which I'm not) Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-244980 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
July 9, 201015 yr Author comment_245031 Thanks all. I needed to set the zone as "Guard Access", which automatically sets the "Access" attribute, and then set the Entry/Exit 2 attribute. Works great now. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29311-texecom-guard-access-zone-causing-alarm-on-pt-set/#findComment-245031 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post