I've finally gotten round to putting the recessed door contact (Knight A51MULTI G2) for the entry/exit rather than using the hallway PIR.

 

I wired everything up and re-enabled zone 1 but it was displaying tamper. So I stripped back the contact and tested all the resistances 2.2 secure, 6.9 active, 1/0 tamper. I also checked the resistances at the alarm box to make sure I didn't have a break in the cable.

 

To confirm I linked the contact circuit into Zone 6 which was spare and wintex diagnostics registers 2.2 secure (healthy).

 

Finally to confirm Zone 1 I bridged and programmed zone 1 to always closed which returned an active state (unhealthy)

 

Does it sound like Zone 1 is dead and I need to replace the board or could it be a common faults that can be rectified without a board replacement?

Edited by jkno
Link to comment
Share on other sites

Yep it's sent to Double Pole/EOL like all the other active zones.

 

It doesn't seem to register the bridge I've put in whether it's open or closed.

 

I've stuck the multi meter across zone (no circuit wired up) and it registers as an open/broken circuit. 

Link to comment
Share on other sites

I didn't wire a resistor over over the terminals but did confirm the circuit was the correct resistance with the multimeter. I also wired a bridge over and switched it to an always closed circuit which it was registering as open (active).

 

I've emailed texecom I expect it's an replacement board job.

Link to comment
Share on other sites

Just to remove any confusion all zones are FSL the contact circuit I want on zone 1 registers at 2.2 secure 6.9 active.

 

As part of my investigation after ruling out any fault at the contact or circuit I remove the circuit from the zone, bridged and reprogrammed as always closed. The zone isn't registering the bridge and thinks its open/active.

 

I'll try a 2.2 resistor just to confirm but think it will be futile because the contact circuit was confirmed with the multimeter at 2.2 and a basic bridge on always closed isn't registered meaning something isn't right on the zone.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.