  1. The co seems to be doing things by the book tbf there replaced the panel etc they have offered maybe gsm or red sec on radio for no extra not sure why the phone bills would be excessive as there's no need for op/cl etc and if keyholder only no need for 24hr test maybe the signals are being aborted via the arc

  2. if you've changed ion to hpo you will have to change  programming in consys or you will get id  faults, also any faulty device on the loop can cause low and high id faults on other devices, a faulty mcp causing id faults is common only way to prove is to discon one device at a time and link the loop thru and check the levels unless you have a shorting device which speeds up the process its  a pain of a fault to trace 

×
×