November 1, 20178 yr Author comment_470630 Nova- groups are disabled, offending zone isn't on soak Al- sorry mate, I wasn't being very clear...I wasn't near a keypad so connected up to the panel and used RSS with the virtual keypad, no luck so tried a physical keypad Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470630 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 1, 20178 yr comment_470635 So, two possibilities? It's either a faulty PCB, or some (corrupt) setting that you're re-loading in with RSS after defaulting. I would try loading the config on a test panel and ensuring that it's not something being held in the config before going through the hassle of replacing the panel PCB. May be worth having a look at the RSS roll-back points and checking the diffs. If you want to duplicate the site in RSS, then change the PIN's to default and send the mdb file to me, I can load onto a test panel here in my office and quickly check it for you if you want. I have all Dimension variants plumbed in and sitting on test at the moment. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470635 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 6, 20178 yr Author comment_470743 Thanks for the offer GalaxyGuy, I have tried it on our demo board 48 and it appears to be fine. I've also been back to site and defaulted the panel, tried setting from a default and it's still showing. Looks like it's time to change the panel. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470743 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 6, 20178 yr comment_470750 I've not seen a zone fault auto omit without also indicating the fault with the zone and asking for confirmation. Assuming that the resistances showing on the panel bang on 1k/2k when you press the hash key. It's a strange one. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470750 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 6, 20178 yr Author comment_470751 Us neither, will keep you updated! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470751 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 6, 20178 yr comment_470753 1 hour ago, GalaxyGuy said: I've not seen a zone fault auto omit without also indicating the fault with the zone and asking for confirmation. Assuming that the resistances showing on the panel bang on 1k/2k when you press the hash key. It's a strange one. Version 5.20 G3-48 did do forced omits on open or faults without any confirmation, took a while for honeywell to believe us Edited November 6, 20178 yr by Nova-Security www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470753 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 8, 20178 yr comment_470797 Sounds daft but have you let the system set with the circuit omitted, Then unset it? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470797 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 8, 20178 yr comment_470799 On 11/6/2017 at 19:24, Nova-Security said: Version 5.20 G3-48 did do forced omits on open or faults without any confirmation, took a while for honeywell to believe us Had this first on an ATM room, I'd replaced the controls and it was on a shunt lock, by the time the lock was thrown it omitted both DT's in the room. You could hold the door open and it would set on the lock, omitting the door too iirc. Nothing is foolproof to a sufficiently talented fool. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470799 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
November 8, 20178 yr comment_470802 Had it where a RIO had been damaged and the system had Call Alarm Co on the keypad but would still set with RIo missing and override the remote reset, Galaxy tech came to site as they didn't believe it. Firmware updated all fine. www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/41691-galaxy-48-zone-omits-when-setting/page/2/#findComment-470802 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post