  1. With zones set to NC, you then consume two zones to cover zone and tamper circuits. This is a bit of a waste of zones when you can cover the tamper open/short circuits with the addition of resistors.
  2. You can set the Galaxy zones to N/C like your old system. Each zone can be programmed individually on Dimension and Flex. I would recommend reconfiguring with new sensors or the addition of resistors (I've never had a problem adding 2x 1k resistors in existing sensors for double balanced zones). It may be worthwhile changing the PIR's anyway, as they're very cheap and the pyroelectric element in the sensors do deteriorate over time reducing their sensitivity.
  3. I only have FX100+ PCB's at £90 + £5 delivery. PM me to arrange if you want. Otherwise, the boards aren't sold separately and you'll need a complete panel.
  4. One ISP is my broadband and the other is the mobile provider, so yes not the same provider for me.
  5. On my own system, with dual path IP at the router level, it just doesn't go down, so there aren't any annoying Comms messages. I only worry when I get an intrusion signal or polling failure which means both paths are down and I really need to take action. Hasn't happened yet. Touch wood. Any messages for one of the paths going down would just be extra nuisance due to ISP reboots, temporary mast issues and the like. I see installers moaning about this sort of thing all the time on FB installer forums. I'd much rather have a multi failover IP path that then relies on very short poll
  6. My thoughts on this are to have a battery backed GPRS capable router in a secured location. This offers better future proofing, as it's not just the alarm that needs to keep communications up if there's a broadband / phone line issue. There's CCTV, HA and more. It's more efficient to have an unlimited data SIM, rather than 3 separate SIM's to track and pay for. It's also easier to keep up with the latest tech. I'm already 5G capable - just waiting on my area being upgraded. If your hone network has its own failover, then all you need is polled monitoring with a decent polling int
  7. It doesn't perform set/unset with Galaxy programming. It only performs silent pa. The Selfmon solution is part of home automation integration, so requires mqtt broker etc.
  8. Where do Honeywell say that? Not for Galaxy anyway... Perhaps Domonial. The only way to do it with the flex is with the Selfmon vmod and an automation platform like home assistant / node red etc. The vmod reads any button press to mqtt, so you can then map it back to set the system.
  9. No reboot is required when changing 51.82. Change 51.82 to DC. Using menu 53 program output *99 to something like strobe. Leave at the default which should be L (Latching) POS (positive). Using test option 32, test the strobe output. Measure with your meter on +12V and OP3. The voltage on OP3 should drop to 0V resulting in the meter reading +12V. If this does not happen, then OP3 is faulty - replace the PCB or add a RIO to gain 4 outputs.
  10. Did you change menu 51.82 to change OP3 to: 2 (DC Output) ? The default for OP3 is as an audio output. The trigger module consumes OP1 and OP2, using these signals to multiplex several outputs. Those outputs include new OP1 and OP2 and the 8 trigger outputs. The trigger outputs are low current, but capable of driving a dialler.
  11. I would agree with this. If you don't keep your phone up to date, or buy the latest model and the app isn't kept up to date, then the chances of issues are high. If you have a look at a few apps reviews, you'll soon see posts of unhappy users where phones and OS versions no longer work. As a an app developer myself, I am often forced to update the app in order to keep provisioning on the stores. Some of these forced updates end up dropping support for older devices, leaving users with very old devices none too pleased.
  12. Personal experience. What aspect ?
  13. The Honeywell Galaxy Flex gives all this. Honeywell provide the flash upgrade program and firmware on their website without any login account requirement too. The app and push notification is free and there are low cost alternatives in the event that Honeywell do start charging. Look out for other offerings that integrate cloud services tightly with the panel, as they may not charge at the moment, but you could find yourself held over a barrel in the future.
  14. This has nothing to do with manufacturing quality. It's a country specific setting and depends on the country code / settings selected. OP, if you have picked up a second user panel, set it to factory defaults using menu 51.17 - cold start. If the tamper still exist after that (with the link fitted), then the panel has a fault.
  15. You need to program a link from the silent PA output to the bell output. This will not work on a trigger output, it needs to be a proper output.
×
×