Cat5


esp-protocol

Recommended Posts

Its ok for camera telemetry, whats it for?

The opinions I express are mine and are usually correct!

(Except when I'm wrong)(which I'm not)

Link to comment
Share on other sites

technically its ok but as its solid core it isnt designed for our terminals. Is used prefer not to but i dont see a real technical reason (the twists are right) apart from it not being screened but technically a balanced 485 shouldnt need screening anyway (i said 'technically' guys)

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Link to comment
Share on other sites

Can any clever person tell me whether they would use cat5 cable on an RS 485 network??

The runs are not particularly long (typically 25m between devices) but it is in a crowded computer room.

Thanks

Dave

For RS-485 the terminating resistors have to match the cable impedance, so you might cause problems unless you get them both right. :whistle:

Read this: http://www.maxim-ic.com/appnotes.cfm?appno...63&CMP=WP-1

Link to comment
Share on other sites

Well....

Its being used for a small BMS system to monitor room temp and humidity stats, and a lot of volt free contacts, we are also picking up some display meters using modbus.

We were goiing to use a two pair twisted individually screened cable but the main contractor has now supplied cat 5 cable and I was just trying to head off any forseeable problems.... thanks

Link to comment
Share on other sites

We recommend it.

Ours is a full duplex (two channel, four core) RS485 bus which runs at over 100kbaud. We have tested it extensively, and it works over 1,000m with Net2. Having said that, all systems are different in the way in which they cope with data errors, so trying it is good.

A useful tip is to connect spare pairs in the CAT5 cable as if they were a screen. That is a very effective method for reducing interferance.

Drew Hoggatt

Managing Director

Paxton Access Ltd

Follow this link for important legal information

Link to comment
Share on other sites

We recommend it.

Ours is a full duplex (two channel, four core) RS485 bus which runs at over 100kbaud. We have tested it extensively, and it works over 1,000m with Net2. Having said that, all systems are different in the way in which they cope with data errors, so trying it is good.

A useful tip is to connect spare pairs in the CAT5 cable as if they were a screen. That is a very effective method for reducing interferance.

cheers drew,,,, a top tip that I will be sure to remember.... thanks