Galaxy Dimension + V-Plex C090 (V1.01): DT7500SN / IS2500SN only report tamper, never alarm – firmware update?
Hi all,
I’m bringing back into service a Galaxy Dimension GD-96 (firmware V6.70) in a house that was renovated 12 years ago. Running a cable to every detector wasn’t possible, so V-Plex (2-wire) was chosen – back then it was the only 2-wire option. It was never commissioned, and now I need to make it work.
Setup
V-Plex Interface C090, firmware V1.01 (shows as RIO 202-205 on line 2), loop OK at ~10.3 V.
Devices: 4191SN contacts, DT7500SN, IS2500SN-type PIRs (4 DIP switches, no microwave), FG-1625SN glassbreaks.
What works
4191SN contacts: zone opens/closes correctly.
All devices learn fine (serial captured when the PIR goes red or a door opens).
Tamper from DT7500SN and FG-1625SN reaches the panel (zone shows open-circuit tamper when the cover is removed).
What doesn’t
DT7500SN / IS2500SN: the alarm never reaches the panel – zone always “closed”, nothing in the log, nothing in Walk Test (31), not even with the system set. Sensor LEDs work normally. Tried loop 1 and 2, fast response, a different unit.
IS2500SN-type PIR: zone permanently shows open-circuit tamper even with the cover closed.
FG-1625SN: with the FG-701 the detector enters test mode (green LED), but I haven’t managed to trigger a real alarm (no red LED) without risking the glass, so I don’t know yet if its alarm would pass.
Questions
Is there a newer firmware for the C090 than V1.01, and how is it updated (chip swap?)
Are the “Smart” V-Plex sensors (DT7500SN, IS2500SN) supported by the C090 at all?
Which V-Plex PIRs are known to work with the C090? (I’ve ordered two older Ademco 4278EX-SN to test.)
Any tip to test an FG-1625SN alarm safely?
Thanks in advance for any help.
47 minutes ago, Vtoioo said:
Hi all,
Setup
What works
What doesn’t
Questions
What you check so far ? Did you try addressing it elsewhere where ?
Power readings at the v90?
And so on lots of tings to look at
Where is that dude galaxy guy when you need him ( @Galaxy Guy
Thanks for replying! Here’s what I’ve checked so far:
Addressing
C090 first on line 1 (RIO addresses 3-5), then moved to line 2, RIO addresses 2, 3, 4, 5 enabled → panel shows RIO 202-205, V1.01, 100% comms. No other RIOs on line 2. Line 2 = panel → C090 → TouchCenter (end of line).
Power
C090 fed from a separate Power RIO (P026) AUX output: 13.75 V at the module (61-1-3).
V-Plex loop at the C090 terminals: 10.28 V DC, polarity correct.
Sensors are powered and their LEDs behave normally (PIR goes red on movement).
Tests done
4191SN contacts: open/close correctly → loop and serial entry OK.
DT7500SN: learned by serial (manual and auto-learn, auto-learn captures it when it goes into alarm), Loop 1 and Loop 2, zone response Fast, Walk Test (31), system set → never an alarm at the panel, only tamper (cover off = open-circuit tamper, cover on = closed).
Two different DT7500SN units and two IS2500SN-type PIRs: same result.
So the C090 clearly talks to the detectors (learn + tamper work), but motion alarms never get through. Any idea what else to look at? Is V1.01 known to have issues with the “Smart” V-Plex detectors?
Thanks!
Addressing
Power
Tests done
Thanks!
So what is the zone attribute set as?
Data wiring to each detector correct?
You sure they are enrolled correctly maybe, delete them all off and disconnect all the detectors except one and try to get that to work?
Edited by al-yeti
Thanks again!
Zone attributes: type Intruder (default), resistance 00 (system, 1k fault/BAL), part set on, response tried both System and Fast. Same settings as the 4191SN contact zones, which work.
Wiring: V-Plex is a 2-wire loop (red +, black –) to each detector, polarity checked, 10.28 V at the C090 and the detectors power up normally. The working 4191SN contacts are on the same loop.
Enrolment: Serial Poll, Loop 1 (also tried Loop 2), serial entered manually (7 digits from the label) and also by auto-learn, which captures the right serial when the detector goes into alarm. The C090 shows the zone as programmed (L1).
Good idea about isolating one detector – I haven’t done that yet. I’ll delete all the zones on the C090, connect a single DT7500SN directly to the C090 loop terminals with a short cable (everything else disconnected) and report back.
On 21/10/2026 at 19:41, Vtoioo said:
Thanks again!
Not that it's the problem , why only 10.28v?
And just to be clear it's only the wired detectors that won't alarm?
And wireless that are learned are ok?