Texecom Elite 88 Expander Errors

Featured Replies

1 minute ago, al-yeti said:

I assume this isn't one the old texecom PSU problems ? 

 

As I understand it the PSU comes from Elmdene, when they failed they just stopped producing voltage.

 

1 hour ago, JOHNNYH said:

It is the control panel at set times causing this loss of power, 12V dipping for 50ms at 10 Seconds in to a minute and at 40 seconds in to a minuet

 

Compare it the ones o your the PSU2000XP's ?

 

Mr th2.jpg Veritas God

  • Replies 44
  • Views 14k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • james.wilson
    james.wilson

    Not wishing to get into the debate but   'Proper' gear needs to comply with the product standard (not the install) and part of that is testing the battery OK Most if not all panel will

  • sixwheeledbeast
    sixwheeledbeast

    Well you came asking for help and your disregarding what you are told by people that work with this stuff every day. I have told you how to rule this out and some things to check, there are furth

  • Sorry I disagree-   I've never had any reason to use an oscilloscope on an intruder alarm nor do I need a £500+ multi meter (it would only get lost or broken out in alarm land)   

Posted Images

9 hours ago, JOHNNYH said:

If you know your stuff ? you will know the average person does not own Keysight oscillosope

 

Every possible measurement needed to commission and diagnose an intruder alarm can be done with multimeter

 

If you have property large enough to need 5 expanders & lots of expensive test equipment I would assume some with your qualifications & talent could earn more more doing your own job & pay a proper alarm co. to provide a working complaint system rather faff around wasting time & money doing it poorly.   

 

 

 

 

 

 

Edited by MrHappy

Mr th2.jpg Veritas God

  • Author
2 hours ago, james.wilson said:

if you run it only on the battery does the comms issues stop? if yes psu issue if no not psu issue

 

its definetly not normal

 

 

running on battery, the problem stops, 

 

no dip of 12V at every 10sec or 40sec 

 

the network supply is 100% stable until mains ins applied and the onboard PSU kicks in

 

regards

 

 

1 hour ago, al-yeti said:

I assume this isn't one the old texecom PSU problems ? 

 

I have only just started to evaluate texecom elite 88 so a little new to the scene

 

what was the old texecom psu issues ? 

-

 

image.thumb.png.7c34527c547416c26773017dcfb5e880.png

 

PE 168, now much smaller system than it was for 20 years as a P168, each building has at least 1 psu, cables run under the public roads            

Mr th2.jpg Veritas God

37 minutes ago, JOHNNYH said:

what was the old texecom psu issues ? 

 

spikes killed them, I've done PE24's between Edinburgh & London this yeat & don't go back

 

I also do Euro's & Orisec & don't have ay real issues with anything.

 

Al doesn't do Texecom using more exclusive equipment...

Mr th2.jpg Veritas God

  • Author
20 minutes ago, MrHappy said:

-

 

image.thumb.png.7c34527c547416c26773017dcfb5e880.png

 

PE 168, now much smaller system than it was for 20 years as a P168, each building has at least 1 psu, cables run under the public roads            

 

why on earth is there a 140 network errors ???

  • Author
13 hours ago, sixwheeledbeast said:

Battery load test is done daily with a delay in hours, the duration of this load test is in secs usually 10, it's not software!

You have too much kit on the system, you have used CCA cable which isn't recommended, it's a SMPS so will get choppy under heavy load.

It's my standard kit and it's not normal behaviour so your speaking to the wrong people.

It also sounds like you have bought the kit second hand or old stock and can't get it to work, there is a possibility you've been past off with old stock with a duff PSU being V6.

 

Either way there are clearly installation issues. The kit isn't designed for DIY installation and neither is the Smartcom.

You also need to use a proper multimeter not wintex if your diagnosing this stuff.

 

you have used CCA cable which isn't recommended

 

what cable is recommended ?

 

I have even tried individually screened CAT7  local to the Alarm to expander 1 & 2

 

no difference

57 minutes ago, JOHNNYH said:

what cable is recommended ?

 

I would normally wire intruder alarm data in belden, daisy chained, screened to cabinet (normally 4mm machine screw & nut, floating at last device 

Mr th2.jpg Veritas God

1 hour ago, JOHNNYH said:

 

why on earth is there a 140 network errors ???

 

25+ year old cables, 20year old expanders, cable length, water in man holes, length of time its measured ?

 

its not a problem site,, so never tried to fixe it.

Mr th2.jpg Veritas God

3 hours ago, JOHNNYH said:

running on battery, the problem stops, 

 

no dip of 12V at every 10sec or 40sec 

 

the network supply is 100% stable until mains ins applied and the onboard PSU kicks in

 

regards

looks like a panel / psu problem then. If it stable without the mains.

 

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Create an account or sign in to comment

Recently Browsing 0

  • No registered users viewing this page.

Important Information

By using this site, you agree to our Terms of Use.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.