1 hour ago, Ashton said:

Isn't the ricochet technology licensed by one of the old boys on an agreement with texe bet he's quids in if it is 

Uh, no

amealing@texe.com

Head of Industry Affairs

Visit Our Website
Texecom

I suppose it helps if you know all the features to find the "glitches" then... ;)

 

Now you mention it I understand where you went wrong with your Duress.

PA Alarm would be the correct output to use for a Duress, PA Silent would only trigger on a "silent" zone whereas PA Alarm is any Panic event including Duress, so that's another "glitch" that wasn't.

  • Like 1
  • Upvote 1

Well according to texe support any output type programmed as pa audible pa silent or duress would activate upon a duress code being entered so if your correct you could have saved me the half hour of my time speaking to Anthony and others at texecom trying to work it out 

The old Texe guys left what maybe 10 years ago now? Thinking about 2006

so I doubt there's a connection with Ricochet.

Would it matter anyway?

 

1 minute ago, Ashton said:

so if your correct you could have saved me the half hour of my time speaking to Anthony and others at texecom trying to work it out 

I could of. Yes.

Duress users behave the same way as Standard users. However, Duress users will activate any outputs programmed as ‘Panic Alarm’ or ‘Duress’ whenever their code is entered.  

surely that would be silent or audible though ? 

I agree it doesn't help no. As I say I haven't called Technical in a long time.

Any queries like that feel free to post on here.

But do note there is only so much we can help with on the public forums.

5 minutes ago, Ashton said:

Duress users behave the same way as Standard users. However, Duress users will activate any outputs programmed as ‘Panic Alarm’ or ‘Duress’ whenever their code is entered.  

surely that would be silent or audible though ? 

 

That's the user options, I realised in a latter post it was the programming of the output you had incorrect.

Output or comms channel if EF should be PA Alarm and not PA Silent.

 

Edited by sixwheeledbeast
typo

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.