Hello

Ive installing an Veritas Excel and im running it in EOL mode using

the two resistor technique. All zones are fine except for one zone

where im running two (no other free zones available) magnet switches.

I was instructed that they should be installed as per the picture

attached, the only problem is when both doors are open the panel must

see a resistance of 53kohm and as a result goes into tamper.

Could you please tell me what is the correct way to run two magnet

switches whilst using eol please? Im guessing that the right way would

be to bypass both magnet switches with one resistor instead of two 22k

as per the attached picture?

mags2.jpg

Many thanks

Trev

Link to comment
Share on other sites

Yep you would need one resistor across both contacts-IE either contact opening would introduce the 22k 'active' state+the 10k EOL resistor-the diagram attached doesn't show that though!.

But the install manual does say 'one device per zone' for high security operation using resistors-and is good practice!.

Any other contributions members?regs etc.

Link to comment
Share on other sites

Thanks for the replys, guys.

Ive ran one cable from each mag back to the panel so im guessing this is how yours would look AlarmGuard

EOL1.jpg

This was how i thought it was ment to be done, as i was thinking if they bypassed one of the mags wrong there would be only 11k of shut resistance? Is this a good idea or am i just beeing dumb?

EOL2.jpg

Thanks again for your help

Trev

Link to comment
Share on other sites

Illustration 1 doesn't work.

Illustration 2 does, but you can have just one 22k resistor rather than two at 11k. The outcome would be the same.

.

.

.

PM me for access to the SSAIB members discussion area.

Link to comment
Share on other sites

Illustration 1 doesn't work.

Illustration 2 does, but you can have just one 22k resistor rather than two at 11k. The outcome would be the same.

ahh yes ive just looked and the 22k and 11k are effectivly in parrellel, which would reduce their resistance seen to about 7k

Sorry about that

Trev