August 7, 200817 yr comment_206642 I am working with a Pyronix KX15DT unit and want to understand its workings. There are 6 terminals - 2 for power, 2 for alarm and 2 for tamper. Am I correct in assuming that behind the tamper connection is simply a closed relay point which opens when the unit is opened? i.e. normally closed Am I correct in assuming that behind the alarm connections is a normally closed relay point which opens when the unit detects movement? Ken Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr comment_206646 Hi, the summary you have given is correct. Rich Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206646 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr Author comment_206652 Excellent. Thank you for that Rich. Now, take the situation where I only have two wires going to the PIR (plus of course two for power). I define the Zone in the panel as Dual End of Line Wiring. The panel book advises use of 4K7 resistors for this setup. So the PIR now has a 4K7 resistor in series with the normally closed tamper relay. It has also a 4K7 resistor in parallel with the normally closed alarm contact. Then, if the panel is NOT armed, it should tolerate seeing either 4K7 or 9K4 and not alarm. This is becaues movement may open the alarm circuit. If the panel IS armed, then it will expect to see only 4K7. If it sees 9K4 then it should alarm. And finally if it ever sees open circuit, it should tamper alarm. Have I got all that correct? Ken Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206652 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr comment_206653 yes but are you sure of the values. I thought pyronix eol was 4k7 alarm 2k2 tamper? securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206653 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr comment_206654 Yep again, sounds all good to me,(Apart from the bit where you said 'if it see's no resistance it will come up as tamper')-Don't tell me thats what you were gonna say next ! . Rich. As Redbull suggests check the resistor values-don't know the panel particularly so I can't comment. Edited August 7, 200817 yr by Rulland Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206654 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr Author comment_206655 The resistor values are only determined by the panel. Not the PIR. It doesn't care? The panel manual says 4K7 for each. Ken Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206655 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr comment_206656 it does, ie it is the panel, and sorry i assumed you also had a pyronix panel. securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206656 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr comment_206657 If thats what the panel requires then thats the values set in the devices then. Rich. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206657 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr Author comment_206658 I am the wiser. Many thanks yet again to the community. Ken. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206658 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
August 7, 200817 yr comment_206660 Thats the beauty of a community such as this-ask a question and someone will answer it-we all have certain skills. Any more for tonight or can i go to bed now . All the best. Rich. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/24320-basic-question-about-how-a-pir-works/#findComment-206660 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post