bellman Posted November 8, 2005 Share Posted November 8, 2005 Double up on the 0v so the 0v line uses two wires to minimise on voltage drop effects. Also no-ones mentioned it but the screen should be connected to mains earth at the panel not 0v, also the screen should be continuous throught a cable run and the shield should not connect to any other core including 0v at any point!Im sure Chris Bellman will clarify this for you. Dave. Absolutely 100% correct Dave. Nothing further i can add. Regards Bellman Service Engineer and all round nice bloke ) The views above are mine and NOT those of my employer. Link to comment Share on other sites More sharing options...