5 minutes ago, virdi said:

 

Yes ...I believe so. It also done the funny beep.

The point I of walk testing is to ensure that the detector that is activating is the detector that is displayed on the panel. For example say the garage is programmed in zone 5 and the landing is zone 4. But you accidentally wired the landing in 5 and the garage in 4, when the alarm goes off you will be looking in the wrong place.

  • Upvote 2
7 minutes ago, PeterJames said:

The point I of walk testing is to ensure that the detector that is activating is the detector that is displayed on the panel. For example say the garage is programmed in zone 5 and the landing is zone 4. But you accidentally wired the landing in 5 and the garage in 4, when the alarm goes off you will be looking in the wrong place.

 

Many thanks. I will double check this also.

  • 3 weeks later...

Hi all,

 

This issue finally got resolved .... I replaced the cable from the Garage PIR to the Panel and also replaced the PIR.

 

No more false alarms so far.

 

Thank you to all that helped and advised