Jump to content
Security Installer Community

Zeta Addressable Panel Issues!


Recommended Posts

hi guys i had some call outs to a site which we took over they have three loops on a zeta panel however they started getting devices come up wrong type?and once they do you cant clear it by re learning or powering down.it starting to become frequent with the smoke detectors.but inside these detectors are apollo!any ideas whats wrong?seems like corrupt data.many thanks in advance

Link to comment
Share on other sites

thanks for the reply.

yea its the premier al4.

its a **** panel but very easy to use i learnt it all without any manuals.

its only slightly harder to set up loop relays as they dont work even when there learnt on you have to set up the zone and output type which wasent as straight forward as it could be!

Link to comment
Share on other sites

Archived

This topic is now archived and is closed to further replies.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.