June 24, 201015 yr comment_242960 Hi Just installed a Scantronic 9651 system, once i power it up keypad says version number an is locked out cant enter anything on it or get into engineer mode. Can someone please explain what i could be doing wrong Edited June 24, 201015 yr by machead Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr comment_242962 Sounds like a problem with the keypad wiring on the data side of it (Clk and Data terminals) Double check that you have connected these to the same terminals at the panel and keypad ends. If so, you may have a damamged cable. In that case, try wiring the keypad on a short piece of cable straight to the panel and try again. Trade Member Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242962 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr Author comment_242963 thanks for the quick reply ive tried what u side above an have also belled the cables out an they are fine too! could there be anything else Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242963 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr comment_242964 Do a restart on the panel with the RKP on a fly lead. You say "belled" cables, was that a continuity device or did you use Ohms ? Ohms will be more precise. As above make sure the data lines are correct. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242964 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr Author comment_242965 Do a restart on the panel with the RKP on a fly lead. You say "belled" cables, was that a continuity device or did you use Ohms ? Ohms will be more precise. As above make sure the data lines are correct. Yes just continuity ah didnt check Ohms what reading should i get from 6-core alarm wire? Thanks Edited June 24, 201015 yr by machead Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242965 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr comment_242966 Hi Just installed a Scantronic 9651 system, once i power it up keypad says version number an is locked out cant enter anything on it or get into engineer mode. Can someone please explain what i could be doing wrong is it new, is the tamper closed? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242966 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr comment_242967 Yes just continuity ah didnt check Ohms what reading should i get from 6-core alarm wire? Thanks On a short length.? Almost zero. (i say almost, just in case there are any pedants around). Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242967 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr Author comment_242968 is it new, is the tamper closed? yes its new an has the original little metal links in the tamper an the PA Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242968 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr comment_242970 yes its new an has the original little metal links in the tamper an the PA what about the tamper switch on the pcb? what code are you trying and are you pressing tick after entering the code? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242970 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 24, 201015 yr Author comment_242971 what about the tamper switch on the pcb? what code are you trying and are you pressing tick after entering the code? it wont let me enter anything getting the beeping sound as if am doing something wrong (if that makes sense!) if i reset the panel it lets me enter 5 key presses then starts doing the high error beep again i am pressing 07890 Tamper switch on the PCB can u tell me a bit more detail? Edited June 24, 201015 yr by machead Link to comment https://www.thesecurityinstaller.co.uk/community/topic/29162-scantronic-9651/#findComment-242971 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post