Put a multimeter on the power pair at the keypad end and see if your getting voltage. If you are you have a faulty keypad if not test the panel end as it could be a blown fuse or a faulty cable.

lee

 

Lee Sutton

E-Mail: leesutton@centurianfire.co.uk

Website: www.centurianfire.co.uk

Phone: 0845 094 9870

CENTURIAN FIRE & SECURITY (part of centurian group limited)

as above with a slight difference, 1st check you have 12 volts leaving the control panel from the designated RKP connections, but my guess though is you have not installed the EOL resistor as shown in the instructions and sometimes taped onto the control panel carton.