May 9, 200718 yr comment_165423 Hi Guys Can any one advise me on the best way to assess correct battery rating. We always use 7ah even for systems with an expander and 12 pirs. Is this right? We install mainly Scantronic 9751's in the domestic/new housing market Do you add up all the components and then what? Is there a chart somewhere? Has any one got an easy to work formulae? What the difference between the two bell settings? sab and scb? Best Chris Edited May 9, 200718 yr by ChrisJarvis Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 9, 200718 yr comment_165427 sab=power in alarm drawn from control panel, scb=power in alarm drawn from bell battery, however on both settings power for strobe is usually drawn from the panel. As for battery rating, you need to measure the current drawn then divide the battery Ah by current drawn , this will give you a standby time in hours, if its not enough it needs a bigger battery. eg system drawing 350ma, 7ah battery. 7/0.350=20 hours The opinions I express are mine and are usually correct! (Except when I'm wrong)(which I'm not) Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165427 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 10, 200718 yr Author comment_165538 sab=power in alarm drawn from control panel, scb=power in alarm drawn from bell battery, however on both settings power for strobe is usually drawn from the panel. As for battery rating, you need to measure the current drawn then divide the battery Ah by current drawn , this will give you a standby time in hours, if its not enough it needs a bigger battery. eg system drawing 350ma, 7ah battery. 7/0.350=20 hours thanks for that chris Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165538 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 10, 200718 yr comment_165585 This formula isn't quite right. You cannot completely drain the battery as it will not operate below a certain voltage and it will become damaged if discharged this much on a regular basis. You need to divide the battery capacity by 1.25. So a 7Ah batt is only really good for 5.6Ah. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165585 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 11, 200718 yr comment_165591 This formula isn't quite right. You cannot completely drain the battery as it will not operate below a certain voltage and it will become damaged if discharged this much on a regular basis. You need to divide the battery capacity by 1.25. So a 7Ah batt is only really good for 5.6Ah. i think we are also supposed to factor in a sounder ring time too - like the fire guys - so its more like 12hrs standby plus 20 mins ring - might be the 7amp battery is now only good for 4 hrs - lots of 19amp batteries going in! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165591 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 11, 200718 yr comment_165622 There was a speadsheet on the scanny website that helps you work it out, but you need to register first. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165622 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 11, 200718 yr comment_165629 i think we are also supposed to factor in a sounder ring time too - like the fire guys - so its more like 12hrs standby plus 20 mins ring - might be the 7amp battery is now only good for 4 hrs - lots of 19amp batteries going in! plus the panel has to charge it twice as fast as before - i seem to remember now Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165629 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 12, 200718 yr comment_165688 Standby_Battery_Capacity_Calculation___Fire.pdf This is what we use for fire....you can adapt the figures to suit..... surely you have an official calculation in your BS somewhere for battery stanbby ?? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165688 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 12, 200718 yr comment_165690 Standby_Battery_Capacity_Calculation___Fire.pdfThis is what we use for fire....you can adapt the figures to suit..... surely you have an official calculation in your BS somewhere for battery stanbby ?? sure Jef would know Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165690 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
May 12, 200718 yr comment_165691 sure Jef would know meeeooowwwwww ! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/18961-battery-rating/#findComment-165691 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post