southfield Posted May 25, 2010 Share Posted May 25, 2010 I am having difficulty in setting up this unit. My main exit entry is via zone 5 full set A. At night the main exit rout is via zone 2 and set with B. The problem is that if you enter through zone 5 when part set in B the system does not recognise zone 5 is open. Can anyone help? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/ Share on other sites More sharing options...
IAS Posted May 25, 2010 Share Posted May 25, 2010 I am having difficulty in setting up this unit. My main exit entry is via zone 5 full set A. At night the main exit rout is via zone 2 and set with B. The problem is that if you enter through zone 5 when part set in B the system does not recognise zone 5 is open. Can anyone help? into engineer mode, what does the screen show for zone5 eg - "ER ....... O ....AB"? and what do options 60 - 61 - 62 - 63 - 201 - 202 - 203 - and 204 - show? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239639 Share on other sites More sharing options...
Guest Oxo Posted May 25, 2010 Share Posted May 25, 2010 Or is the zone set as entry on both A and B? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239640 Share on other sites More sharing options...
arfur mo Posted May 25, 2010 Share Posted May 25, 2010 a logical approach will save hours of time and frustration, you might do better using a basic setup and get that working properly before you go on to the more exotic, ie. walk before you run. so forget all the fancy part sets until you get it to work properly as a full on system, check carefully all you detection actually works and they are actually on the zones you think they are - accidental zone cross overs happen to the best' believe me they do and over confidence often leads to the biggest falls. then modify one zone at a time and check the results. regs Arfur Mo If you think education is difficult, try being stupid!!!! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239644 Share on other sites More sharing options...
james.wilson Posted May 25, 2010 Share Posted May 25, 2010 I am having difficulty in setting up this unit. My main exit entry is via zone 5 full set A. At night the main exit rout is via zone 2 and set with B. The problem is that if you enter through zone 5 when part set in B the system does not recognise zone 5 is open. Can anyone help? Are your circuits working correctly, ie does circuit 5 work at any time? securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239656 Share on other sites More sharing options...
southfield Posted May 26, 2010 Author Share Posted May 26, 2010 I am having difficulty in setting up this unit. My main exit entry is via zone 5 full set A. At night the main exit rout is via zone 2 and set with B. The problem is that if you enter through zone 5 when part set in B the system does not recognise zone 5 is open. Can anyone help? into engineer mode, what does the screen show for zone5 eg - "ER ....... O ....AB"? and what do options 60 - 61 - 62 - 63 - 201 - 202 - 203 - and 204 - show? Thanks for getting back. 05:FE a 1 60:B=FE = NA 61:B=ER = FE 62:B=Silent 63:B=Full 201:Entry 1 =10 202:Entry 2 =10 203:Entry 3 =10 204:Entry 4 =10 The above are the numbers as you requested. Regards Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239735 Share on other sites More sharing options...
IAS Posted May 26, 2010 Share Posted May 26, 2010 Thanks for getting back. 05:FE a 1 60:B=FE = NA 61:B=ER = FE 62:B=Silent 63:B=Full 201:Entry 1 =10 202:Entry 2 =10 203:Entry 3 =10 204:Entry 4 =10 The above are the numbers as you requested. Regards okay you havnt selected 5 to be "active" when set option B, should read "5:FE.....AB.....1" if you want the ability to "come in" through that route when set on "B" rather than instant alarm change "60:B=FE=NA" to "60:B=FE=FE" and just a 10 seconds entry time, are you sure? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239749 Share on other sites More sharing options...
southfield Posted May 26, 2010 Author Share Posted May 26, 2010 okay you havnt selected 5 to be "active" when set option B, should read "5:FE.....AB.....1" if you want the ability to "come in" through that route when set on "B" rather than instant alarm change "60:B=FE=NA" to "60:B=FE=FE" and just a 10 seconds entry time, are you sure? Thanks for that. Just changed the item lines you said and all is now working. The entry time is ok at the moment. Again. Many thanks. Or is the zone set as entry on both A and B? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239757 Share on other sites More sharing options...
IAS Posted May 26, 2010 Share Posted May 26, 2010 Thanks for that. Just changed the item lines you said and all is now working. The entry time is ok at the moment. Again. Many thanks. glad to help Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239760 Share on other sites More sharing options...
james.wilson Posted May 26, 2010 Share Posted May 26, 2010 You might want to thank him by giving him a reputuation point securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28976-scantronic-9651-control-unit/#findComment-239762 Share on other sites More sharing options...