Fire Alarm System Into Intruder Alarm

Featured Replies

  • Replies 36
  • Views 8.7k
  • Created
  • Last Reply
  • Author
The wrong buttons :whistle:

clearly ...

That neat little program says I need 13.8aH of backup ... so thats what I will get ... in the form of 2x7aH ... 1 in PSU and the other in main panel.

Sounds good to me. And for a non pro carrying out this work fair play, because there are a lot of engineers out there that would have issues doing this.

Need any help please revisit.

Good luck bud !

  • Author
Sounds good to me. And for a non pro carrying out this work fair play, because there are a lot of engineers out there that would have issues doing this.

Need any help please revisit.

Good luck bud !

Thank you! I appreciate that alot.

I'll be sure to keep everyone informed ... as I run into troubles along the way no doubt.

Just to stop you for a second.

Did you work out the loadings independently for the panel and PSU. As they will not be powering each other under a mains fail.

As you gave a total power consumption in your calculations.

cheers

  • Author
Just to stop you for a second.

Did you work out the loadings independently for the panel and PSU. As they will not be powering each other under a mains fail.

As you gave a total power consumption in your calculations.

cheers

No that was overall.

So the PSU is not wired into the Panel (for power sharing) its just A&B lines linking the two ?

May mean that I will need more backup power in the PSU than in the Panel.

Worst case is that I put the biggest physical battery I can in each of the Panel and PSU.

your 1A galaxy will only support a 7A/h however your 3A smart psu will support a 17A/h

I would load the panel the lightest so that the smart ran out first. YOu can use that application of ours to work out the loading accross each supply

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Archived

This topic is now archived and is closed to further replies.

Recently Browsing 0

  • No registered users viewing this page.

Important Information

By using this site, you agree to our Terms of Use.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.