  1. 7 minutes ago, PeterJames said:

    The point I of walk testing is to ensure that the detector that is activating is the detector that is displayed on the panel. For example say the garage is programmed in zone 5 and the landing is zone 4. But you accidentally wired the landing in 5 and the garage in 4, when the alarm goes off you will be looking in the wrong place.

     

    Many thanks. I will double check this also.

  2. Hi all,

     

    Need some help please.

     

    Me and friend just installed a Premier Elite 48 and placed a Premier Elite DT PIR Sensor in the garage.

     

    However, the Garage PIR is causing false alarms within minutes of arming the system.

     

    We have turned the Microwave sensitivity right down to minimum and changed the Pulse Count Jumper to '2' ...but it's still setting off the alarm.

     

    What's the first thing I can try please?

     

    Could it be cold air blowing through the garage door or vents?

     

    Thanks

     

     

     

×
×