you havnt selected 5 to be "active" when set option B, should read "5:FE.....AB.....1"

if you want the ability to "come in" through that route when set on "B" rather than instant alarm change "60:B=FE=NA" to "60:B=FE=FE"

and just a 10 seconds entry time, are you sure?

Do you really want a silent Alarm in Part set B as well?