April 23, 200917 yr comment_234677 Called out today to an eight zone Sigma CP K fire panel that has a intermittent Earth Fault that can last for a few hours or a few seconds. No zone or sounder fault led's operate just the general fault led. All earth connections have been disconnected but still the fault, any ideas? Could the fault be caused by the mains earth? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr comment_234678 All earths? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234678 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr Author comment_234681 All earths? Zone and Sounder. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234681 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr comment_234682 Have you disconnected the earth lead from the pcb? - Pete Peter Robinson Freelance M:07889038650 Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234682 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr Author comment_234684 Have you disconnected the earth lead from the pcb? - Pete No Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234684 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr comment_234686 did the same myself, thinking old cable etc etc disconnected and fine since (9 months+) ti's all a learning curve Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234686 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr comment_234724 If it stays up then eliminate by disconnecting field wiring per output/input (sounder/zone) - disconnecting panel earth only removes the panels earth fault reference and hasn't cured the fault.If the panel still shows an earth fault and you have eliminated ALL field wiring (inc. mains supply) then the panel is at fault. The fault is there for a reason. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234724 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 23, 200917 yr comment_234726 Back to basics, Quickest way on a small system is to put EOL devices in at panel and prove panel. Then Put each zone/sounder back in one by one. Then you have a reference point. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-234726 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 30, 200917 yr comment_235702 Oxo, its intermitant. if its not there your cant find it. Had a similar problem myself on a much bigger scale with a morley Zx5. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-235702 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
April 30, 200917 yr comment_235705 Oxo, its intermitant. if its not there your cant find it. Had a similar problem myself on a much bigger scale with a morley Zx5. All I suggested was to prove the panel. Then the fun can start, or do you chase your tail for the first hour Link to comment https://www.thesecurityinstaller.co.uk/community/topic/28316-intermittent-earth-fault/#findComment-235705 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post