January 2, 200917 yr comment_219822 i'm just adding an m12 smoke heat detector to my unconfigured eurosec cpx panel. my problem is that one of the config options on the m12 is 'latching reset' or 'auto reset' but which option is compatable with the cpx? thanks for reading!! Link to comment https://www.thesecurityinstaller.co.uk/community/topic/26148-eurosec-cpx-m12-smoke-query/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
January 3, 200917 yr comment_220022 We don't use the cpx panels but do use the M12 smoke det If the M12 is on its own zone you can just set the detector to auto reset if it is sharing a zone you would want it to latch and use an output to drop the 12 supply (detector reset ) www.AllanMoncrieffAlarms.com Link to comment https://www.thesecurityinstaller.co.uk/community/topic/26148-eurosec-cpx-m12-smoke-query/#findComment-220022 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post