Jump to content
Security Installer Community

Emercency Lights


rob walton

Recommended Posts

Hi guys,

Has anyone come across Maintained emergency lights with Time Lag switches trying to start on their own?

I have a fluctuating 120 Volts on the switched live and can't located the cause?

There are 3 fittings and 6 switches on the circuit and some idiot has supplied this through 3 MCB's but the switched live is common to all fittings!

Any ideas?

cheers

Link to comment
Share on other sites

Is it actually on the switched live cable whilst all fittings are disconnected from this cable? If not, then it could be anything.

Need more info really, but I'd be inclined to rewire it before doing anything as it's non compliant with BS7671 or BS5266.

Link to comment
Share on other sites

  • 4 weeks later...

Hmm, maybe it's the self test feature of the light ?

I do have some emergency lights that regularly (approx once a week) light up themselves for a few seconds to test for the battery status and bulb health.

uski

Link to comment
Share on other sites

Archived

This topic is now archived and is closed to further replies.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.