Gent Panel Clicking Every 60 Seconds
in General Fire Alarm Queries
Posted
The relays on the loop cards are isolating relays, it's common for these to chatter on older cards, the firmware versions you are running are ancient ( If a vigilon) also the loop resistance being to low can cause issues on gent systems, a resistor won't fool it as the loop also runs rs485 data, try using a long length of cable coiled up just to create a dummy load, the clicking will be part of the fault monitoring pulse put out in the loop but shouldn't be that noticeable