1) Hello. Situation: we have panel with ADT Minerva MX4000. The supplier delivered to us panel with already addressed sensors 813P, but fire inspection forced to change project (more sensors to install). We employed local company. Enginer spent les than an hour with panel, and said that in second delivery all sensors have standard 255 adress. But they all are already mouted (more than 150 sensors) . He says we should demount them, so he could address them correctly according  to project. I doubt, so now I ask here, is there any possibility to change addresses without demounting sensors from bases?

2) Second thing, he asks is software MX CONSYS. Is it neccessary for him?

Link to comment
https://www.thesecurityinstaller.co.uk/community/topic/39905-minerva-mx4000/
Share on other sites

Hello.

 

The short answer is yes, you do need to remove the sensors in order to address them.  It is possible to change the address of a single sensor from the panel, but if all the sensors are set to 255 then this won't be possible.  Sorry!

 

Matt

Thank you. One doubt less :) And what obout software. Could he change supplier's installed logic from panel, or I need to buy software? You say, that sometimes it's possible even to change addresses from panel, so may be he could to change logic from panel? 

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.