Flying Boy Posted December 24, 2006 Share Posted December 24, 2006 Hi Guys, I have just taken over a Menvier TS2500 and it is a little while since I worked one so I'm after a refresh. 1. I have to do some additonal works on the system can I mix zone wiring types e.g. double pole and eol on the same Node? 2. If I want to add a node in the middle of the network can I address this to be the next avaiable address or does it have to run concurrently e.g.1,2,3,4 3. I programmed an exisiting zone 24hr at the customers request but when I opened the door no noise. I have checked the zone and this is working correctly. I have not entered the zone into a ward as the customer only does full set. Any ideas? for any help Flyingboy Link to comment https://www.thesecurityinstaller.co.uk/community/topic/14259-menvier-ts2500/ Share on other sites More sharing options...
BUSTER Posted December 24, 2006 Share Posted December 24, 2006 1 - Yes 2 - Yes 3 - Zone must be allocated to a ward Any comments / opinions posted are my opinion only and do not represent those of my employer or Company Link to comment https://www.thesecurityinstaller.co.uk/community/topic/14259-menvier-ts2500/#findComment-139947 Share on other sites More sharing options...
Flying Boy Posted December 24, 2006 Author Share Posted December 24, 2006 Thanks alot for the help have a good christmas Flyingboy Link to comment https://www.thesecurityinstaller.co.uk/community/topic/14259-menvier-ts2500/#findComment-139948 Share on other sites More sharing options...