June 10, 200619 yr comment_102390 I'm trying to get a digicom programmable output to go 0v when a fire zone is activated or fire on keypad is pressed. I'm using wintex to program. So far I have output 1 programmed as areaD (which the fire zones are assigned to), and set as option 11 fire. The voltage doesn't change on the output when fire is activated. Have tried changing to PA and when I press PA on the keypad the output goes 0v, but as soon as I go back to fire on that output nothing happens. Anyone got this working? Link to comment https://www.thesecurityinstaller.co.uk/community/topic/10897-premier-48-digicom-outputs-for-fire-detection/ Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post
June 10, 200619 yr Author comment_102396 Doesn't matter guys, sorted it. Had to enable "unarmed fire comms" in Area options otherwise the output only triggers when system/area is armed. Link to comment https://www.thesecurityinstaller.co.uk/community/topic/10897-premier-48-digicom-outputs-for-fire-detection/#findComment-102396 Share on other sites Share on LinkedIn Share on X Share on Facebook {lang="reddit_text" Share via email Share on Pinterest More sharing options... Share this post