Hi everyone,
I have a problem with my house alarm system, the external box does not make any noise when the alarm is triggered. This only came to light recently on entry to the house (when the alarm was set), we didnt reach the control panel in time. The internal sounder went off, nothing from the external one.
The control panel is a Veritas Compact 8 which was installed in 2003/4 to replace an existing antiquated panel. Everything else works fine, internal sounder, setting/unsetting of alarm, using the various zones, etc. It's just the outside box that's the problem.
I've gone through the various trouble-shooting exercises shown in the user/installation guide, but to no avail. However, when I removed the fuse for the external sounder from the control panel it went off ! So it obviously works, just not when it should..
Any ideas what the problem could be?
Thanks.
Not certain on the Veritas but other panels (including Texecom Premier series) have an option were only Internal bells will sound if its an entry alarm (only sensors on entry route activated) rather than a full alarm
hope that helps
External Sounder Not Working
in General Security & Fire Queries
Posted
You said in first post that the Bell activates when you removed the power from the bellbox. - So it seems to be self activating ok.
That then suggests the trigger from the panel is not working right, either bad connection/short between trigger and -12v (for negative tamper) or perhaps bell is set for neg trigger when panel is positive (or vice versa - though perhaps more likely to have a constantly wailing bellbox if this was the case, I've never tried this, either accidently or on purpose).
You could test the trigger in the panel with a multi-meter to check its changing/sending correct signal when bell activated, however thats assuming that you installed the panel and are confident opening it up and using multimeter.
CDJ