1 hour ago, james.wilson said:
the viper will flash like that its a 'comfort' led if you tap them again the led will stop for about 7 sec. Best to have them in this mode its like comfort leds on a bell, shows its powered
Can the led’s be turned off ?
-
46 minutes ago, sixwheeledbeast said:
Nope, use the Texecom Impaq ones unless I have to use proper Vipers for replacement (aesthetics/latch line etc)
Mostly wireless shocks now if customer needs perimeter.
They havent been triggered in a very long time maybe since they have been installed. Alarm will set and unset as normal and will trigger if they are bashed or knocked.
-
1 hour ago, sixwheeledbeast said:
They flash red all the time with comfort on, latch line is solid light
They only started flashing when i tested they were working the other day.
-
I can remove the battery backup and turn the power off to the panel. You think that would reset them ??
-
Small bit further help. After getting the PIR sensor installed and working. I decided to do a walk test and see if everything was fine and which zones were which.
I believe these are shock sensors ? well i gave them a little nudge to see which zone they were in and now they flash red constantly. Anyone any ideas how to get them to stop flashing ???
I have set the alarm and unset it ive been into engineer mode and done a reset still they flash ALL NIGHT LONG !!
Any further help would be appreciated......
-
Thanks to all the replies.
PIR now working perfectly few issues I forgot I set the alarm to all the defaults so not knowing the default pin was #### i triggered the tamper and couldn’t shut it down but got it all done in the end.
-
3 minutes ago, al-yeti said:
Mogadishu is safer to travel to than ardossan
You would be required to wear a Haz mat suit at all times and that was before COVID-19
- 1
-
Iron brew for the hangover. But beer to cause that effect
-
19 minutes ago, al-yeti said:
I guess I could type it out but I am going to be lazy , your just getting confused the word eol , ignore it , so then instructions are the same as what I said before
White and green to tamper terminals
Blue and yellow to alarm terminals
Black is minus - terminal
Red is positive + terminal
Thanks for the help. I owe you a few of these
-
So don’t put any cables in the EOL screws ?
-
2 minutes ago, al-yeti said:
White and green to tamper terminals
Blue and yellow to alarm
Black is minus -
Red is positive +
Aux DC fail because probably short it out
On the new PIR it has two connectors for Alarm and tamper one each with EOL above them what colour in the EOL screw
+ Red
- Black
Alarm EOL ?
Alarm ?
Tamper ?
Tamper EOL ?
thanks for all the help and patience and yes the glass fuse is blown I will replace it
-
-
Lets pretend im stupid
What colour wires go into the pyronix terminals ??
And since ive cut the old one off now the panel is saying AUX DC fail ?? Am i better getting a pro into look at it ?
-
Hi all hoping someone on here can help and save me trying to get someone to fix this. We have had a new kitchen installed and the fitters cracked the sensor off the wall and ive got a new one can someone help me ?? which wires go where on the new one ?
The sensor on the left is the old one and the sensor on the right is the new one Pyronix KX10DP. Do i need a different PIR sensor ???
Any help would be greatly appreciated
Help please
in Introduce Yourself
Posted
Do you know how to turn them off ? Have they got jumpers within the shock sensor ?