  1. Hi,

     

    I have a Flex20 and just got my hands on a slightly second hand CP045 Touchcenter.  Trouble is, It defaults to French and when powering up, it should take me to the addressing page so I can get it to talk properly with the Flex.  Unfortunately, it doesn't come up with that - just straight to the home page.  

     

    Anyone any ideas how to factory reset it so I can set the address (and language)?

     

    TIA

     

  2. On 02/08/2019 at 09:09, al-yeti said:

    1. Yes you need port forwarding or update IP manual each time, unless Honeywell have got there act together?

    2. No better get installer to update firmware

     

    You could try selfmon service instead can work in conjunction with your gx app

    I am the installer here but many many years since I've done a panel firmware update..

  3. Hi everyone; thanks for reading.

     

    I have installed a Flex 20 and have many modules - including the ethernet module.  I now have the GXRemoteControl app and have it set up, working on the home WiFi network.  Now, 2 things:

     

    1. I can't access outside on my home network - Do I need to set up port forwarding or similar on my router?  I don't have a static IP - is this an issue?  Maybe wrong settings on the app.

     

    2. When using the app, pressing the 'outputs' tab, it tells me I need to update the firmware.  Under 23/ Version shows as 1.10.  Is it easy to update this myself?  I tried to download from Honeywell but don't think it woks with Mac...

     

    Any advise gratefully received :)

  4. On 27/02/2019 at 23:45, GalaxyGuy said:

    Okay, checked this out on the Flex with a RIO.  So what you need to do is configure the virtual RIO in the RF portal so that it doesn't take any addresses up.  Ie. No virtual RIO enabled. Then you can configure any of the 20 hardwired zones as either wireless or hardwired.  The easiest way to do this is to:

     

    1. Enter engineering mode and remove both portal and rio from the system.

    2. Exit engineering mode and remove the devices from the config when prompted.

    3. Set the RIO address to 2 and add back to the bus.

    4. Enter eng mode and menu 72 to detect the device.

    5. Add the portal and then menu 72 to detect it.

     

    Now the portal should show on its bus, but with no virtual RIO's addressed (menu 51.60.1 shows the virtual RIO - note my typo earlier when I said it was 56).

     

    If you want to do this without removing devices, you need to use 51.60.1 to diable the virtual rio, then the hard wired RIO can be enumerated onto the bus.

     

     

    I had exactly the same issue.  Thank you so much for sharing. Now I just need to work out how to use the Ethernet module to connect to the app...

×
×