can any one help me with a new panel i have to fit its a premier 48 panel that needs to switch on some flood lights when the zones are entered has 16 jones as guard 1 as guard accress and 1 as entry / exit all to switch lights on when the system is set only

but needs to go active when some one goes though any zone but before the alarm goes into alrm state????.

Wayne Hibbs

Link to comment
Share on other sites

i have fitted a premier 48 panel and need some help set up the panel output to drive 12 v relays conected to flood lights 1 have all relay up and running and now need to program the outputs. so that any zone entered will switch on the outputs . but before the alarm goes active there is a total of 18 zones i have set 1 zone as entey / exit (delay 30 seconds) and the rest of them are set to guard what is the best setting to use

i have looked at setting the output to entey/ exit but only works on 1 zone

also i tried setting it to the output to alarm but it will not switch relays on the entry zones unless the entey timer ends. please help me thanks

Wayne Hibbs

Link to comment
Share on other sites

now im confused i thought this was answered. I think to avoid confusion you need to lay down exactly what you want to achieve. All the info, dont leave out anything you dont think is relevant mate

sorry posted wrong topic sorry

Wayne Hibbs

Link to comment
Share on other sites

from duplicate post you want lights to activate for 3 minutes when any zone is triggered including entry/exit when armed.

One problem you have is telling the system that it is actually night, you can program a timer but its dark at 10pm in summer and 4pm in winter.

You can get daylight sensors that have double pole relays in them, try maplins.

Even if you do wire in a daylight sensor you will then need to program a custom output so the output activates

When its dark AND The system is set AND (When its in alarm OR In entry)

Then you need to set a pulse period of 3 minutes for the output

The opinions I express are mine and are usually correct!

(Except when I'm wrong)(which I'm not)