Hi

I have recently bought a Risco Lightsys2 system to replace my existing system. (detectors wired independently with 6 core cable)

I can see the PIRs are now EOL however the PIR's I have are standard 6 contact Risco RK500q.

Any help would be really helpful.

Thanks Mike

Link to comment
Share on other sites

Hi, use N/C (01) for zone 1-7 for alarm contact and zone 8 for common Tamper (for Z 1-7).

You can view  this is also in the installation manual ?

Good luck.

 

Termination

 

 

 

 

Termination

 

 

 

The Termination menu enables you to program the connection type used for each of the system's zones. The actual (physical) termination for each zone must comply with that selected in the zone termination menu

N/C

 

 

 

Uses normally-closed contacts and no terminating End-of-Line Resistor

EOL

 

 

 

Uses normally-closed (NC) and/or normally-open (NO) contacts in a zone terminated by End-of-Line Resistor.

DEOL

 

 

 

Uses normally-closed (NC) contacts in a zone using End-of-Line Resistors to distinguish between alarms and tamper conditions.

N/O

 

 

 

Uses normally-open contacts and no terminating End-of-Line Resistor.

 

 

Link to comment
Share on other sites

It was not quite right with Paste/cut, this is maybe more clearly.

 

Quick Key           Parameter

212 5             Termination 

                      

The Termination menu enables you to program the connection type used for each of the system's zones. The actual (physical) termination for each zone must comply with that selected in the zone termination menu

 

01                           N/C

                                    Uses normally-closed contacts and no terminating End-of-Line Resistor

 

02                           EOL                        

     Uses normally-closed (NC) and/or normally-open (NO) contacts in a zone terminated by End-of-Line Resistor.

 

03                           DEOL                     

     Uses normally-closed (NC) contacts in a zone using End-of-Line Resistors to distinguish between alarms and tamper conditions.

 

04                            N/O                       

                                Uses normally-open contacts and no terminating End-of-Line Resistor.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.