rossibufc 0 Posted April 2 Share Posted April 2 Hello everyone. Long time since I have been in here but could one of you fine fellows answer a question about a Pyromix Euro 46. Can the panel be 4 wire and say the expanders be EOL. Would get me out of a big hole if it could. Cheers Quote Link to post Share on other sites
MrHappy 1,864 Posted April 2 Share Posted April 2 yes Quote Mr Veritas God Link to post Share on other sites
james.wilson 783 Posted April 2 Share Posted April 2 bear in mind any eol panel that doesnt use pos and neg circuits (none do that i know of?) dp wiring wont comply as it wont detect a short circuit Quote securitywarehouse https://store.securitywarehouse.co.uk Trade Members please contact us for your TSI vetted trade discount. Link to post Share on other sites
MrHappy 1,864 Posted April 2 Share Posted April 2 1 hour ago, james.wilson said: (none do that i know of?) unless I'm mistaken- Eur Mini has neg gobal tamper & positive loops (you loose a zone this way) Eur 46 has pos / neg loops on on endstation Double pole expanders are available Premier 48,88 & 168 & std expander are double poled with EOL on the outer zone pair (like TS Networker) Quote Mr Veritas God Link to post Share on other sites
rossibufc 0 Posted April 2 Author Share Posted April 2 Cheers fellows. Quote Link to post Share on other sites
james.wilson 783 Posted April 2 Share Posted April 2 6 hours ago, MrHappy said: unless I'm mistaken- Eur Mini has neg gobal tamper & positive loops (you loose a zone this way) Eur 46 has pos / neg loops on on endstation Double pole expanders are available Premier 48,88 & 168 & std expander are double poled with EOL on the outer zone pair (like TS Networker) Sorry I was using my galaxy and old euro knowledge was off then Quote securitywarehouse https://store.securitywarehouse.co.uk Trade Members please contact us for your TSI vetted trade discount. Link to post Share on other sites
Amps 47 Posted April 3 Share Posted April 3 18 hours ago, james.wilson said: bear in mind any eol panel that doesnt use pos and neg circuits (none do that i know of?) dp wiring wont comply as it wont detect a short circuit Douple Pole is ok for Grade 2 is it not? Quote Link to post Share on other sites
sixwheeledbeast 541 Posted April 3 Share Posted April 3 Yer, G2 but only if it can detect a short like JW says. Quote Link to post Share on other sites
Amps 47 Posted April 3 Share Posted April 3 9 hours ago, sixwheeledbeast said: Yer, G2 but only if it can detect a short like JW says. So Euro 46 double pole does not comply? Quote Link to post Share on other sites
james.wilson 783 Posted April 3 Share Posted April 3 It was never designed for dp the older stuff was and had pos and neg circuits iirc odds were neg evens were pos. Quote securitywarehouse https://store.securitywarehouse.co.uk Trade Members please contact us for your TSI vetted trade discount. Link to post Share on other sites