xpertalarms Posted May 21, 2020 Share Posted May 21, 2020 Got a galaxy dimension that activates fine on all groups apart from one group...sounders assigned to that group don't activate but comms goes through fine. Had a look at all the group parameters and output programming but can't see anything out of the blue. Any suggestions? Thanks Quote Link to comment Share on other sites More sharing options...
al-yeti Posted May 21, 2020 Share Posted May 21, 2020 36 minutes ago, xpertalarms said: Got a galaxy dimension that activates fine on all groups apart from one group...sounders assigned to that group don't activate but comms goes through fine. Had a look at all the group parameters and output programming but can't see anything out of the blue. Any suggestions? Thanks How is the setup? How many groups and all Sounders seperated to each group? Or you saying common sounder doesn't activate or output only for that group doesn't activate 3 minutes ago, Logan said: I only know galaxy 60 unfortunately Come on Logan you don't know the galaxy 60 ? Quote Link to comment Share on other sites More sharing options...
xpertalarms Posted May 21, 2020 Author Share Posted May 21, 2020 (edited) The setup has 1 building with 2 groups, and 1 building with 1 group. The building with 1 group is seperate to the main building, with the exception that the keypad in the main building is assigned to all groups. Sounders are seperated per group. Edited May 21, 2020 by xpertalarms Quote Link to comment Share on other sites More sharing options...
al-yeti Posted May 21, 2020 Share Posted May 21, 2020 Hmmm need expert nova? SW? You sure you wired it up correctly? And assigned correct output to that group? Easily missed if not your regular panel Quote Link to comment Share on other sites More sharing options...
xpertalarms Posted May 21, 2020 Author Share Posted May 21, 2020 Yep all wired correctly, correct outputs assigned. I've done an output test too and that's all fine. Very strange..... Quote Link to comment Share on other sites More sharing options...
al-yeti Posted May 21, 2020 Share Posted May 21, 2020 38 minutes ago, xpertalarms said: Yep all wired correctly, correct outputs assigned. I've done an output test too and that's all fine. Very strange..... So your saying only alarm.condition fails to trigger out put? Quote Link to comment Share on other sites More sharing options...
xpertalarms Posted May 21, 2020 Author Share Posted May 21, 2020 Yep, outputs are fine otherwise Quote Link to comment Share on other sites More sharing options...
Nova-Security Posted May 21, 2020 Share Posted May 21, 2020 If the outputs are assigned correctly for that area have you got a bell delay programmed What does not sound e/e or alarm tones ? Quote www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment Share on other sites More sharing options...
xpertalarms Posted May 21, 2020 Author Share Posted May 21, 2020 No bell delay programmed, ee tones are fine on both the keypad and ee horn for that group, but neither of them sound during alarm and the bells output type doesn't either Quote Link to comment Share on other sites More sharing options...
james.wilson Posted May 21, 2020 Share Posted May 21, 2020 51 17 Id go for a restart first how is the output programmed ie group * modifier etc Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment Share on other sites More sharing options...
al-yeti Posted May 21, 2020 Share Posted May 21, 2020 1 hour ago, xpertalarms said: No bell delay programmed, ee tones are fine on both the keypad and ee horn for that group, but neither of them sound during alarm and the bells output type doesn't either Can you get a fourth group to output correctly? Quote Link to comment Share on other sites More sharing options...
xpertalarms Posted May 21, 2020 Author Share Posted May 21, 2020 Tried a restart @james.wilson. there are 3 outputs programmed as bells, strobe and ee horn all assigned to A3 only without any modifiers. @al-yeti might try this, A1 and A2 work fine in the main building. Thanks Quote Link to comment Share on other sites More sharing options...
al-yeti Posted May 21, 2020 Share Posted May 21, 2020 It's a d48? Quote Link to comment Share on other sites More sharing options...
xpertalarms Posted May 21, 2020 Author Share Posted May 21, 2020 Just now, al-yeti said: It's a d48? Yep Quote Link to comment Share on other sites More sharing options...
Nova-Security Posted May 22, 2020 Share Posted May 22, 2020 (edited) Have a look at group status 53 - 7, should be a - for outputs to work all the time Edited May 22, 2020 by Nova-Security 1 Quote www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment Share on other sites More sharing options...
xpertalarms Posted May 22, 2020 Author Share Posted May 22, 2020 7 hours ago, Nova-Security said: Have a look at group status 53 - 7, should be a - for outputs to work all the time That'll be the one. All sorted now, thanks @Nova-Security Quote Link to comment Share on other sites More sharing options...
Nova-Security Posted May 22, 2020 Share Posted May 22, 2020 Glad it worked Quote www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment Share on other sites More sharing options...