I was working on a TS690 this afternoon and I set up a new ward partition C. However when i trigger a device in that ward it is not registering an alarm not audible or even in the log.

 

If i full set the premises everything works as it should. I have looked in the menu option 'configure wards'.

 

Any ideas?

Link to comment
Share on other sites

Is the 690 not programmed the opposite to what you normally do in that the zones you think are included are excluded, I'm sure I had this years ago and that was the only way I got it working

Trade Member

Link to comment
Share on other sites

On 30/06/2018 at 10:22, sixwheeledbeast said:

It's likely the part sets are set incorrectly.

You have to both configure the Wards included and configure the zones included for in that ward separately.

 

So one you've congifigured your new ward C added what circuits you want into that zone... what is the next step? The menu option configure wards seems to have limited options not a lot you can add/change.

 

Thanks

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.