Look at the 485 protocol it will show it's needed. Plus as above you link negs on cameras. Trust me 485 does not need a common to work. Other stuff does but not the data

Firmware is irrelevant

Don't get me wrong its good advice to prevent switching issues, but isn't needed for just data

I wouldn't as a rule common negs unless switching outputs across expanders. Electrical isolation is preferable imo

but thats the whole point of rios lims zems etc,might as well wire everything back to the panel if your worried about phase issues

Link to comment
Share on other sites

And then you data line out is taken from the ethernet module ?

 

Must be, as it doesnt work on remote buildings unless common the negs, may be as they are not on the same supply.

Good point 

No the data out isnt taken from the ethernet module.

I have two data lines connected directly to the control panel and i have the ethernet module plugged onto the 4 pins.

Do you think this could cause the problem?

Link to comment
Share on other sites

Well if you remember I had this issue with a 520 , a line dropping some modules , and only thing I found was the neg problem since then been a while the problem hasn't surfaced

ah well the one 520 you couldnt fix and dissed a neg didnt fix the cause did it,so was it a phase problem or a supply problem or something else

Link to comment
Share on other sites

Good point 

No the data out isnt taken from the ethernet module.

I have two data lines connected directly to the control panel and i have the ethernet module plugged onto the 4 pins.

Do you think this could cause the problem?

 

No the length is too short and the bus too resilient for this to be an issue. But if Ethernet COM4 is dropping out too, then it rules any open on the bus out.

 

It would appear that something is dragging the bus down. A slave device can do this if it sits in write mode when it shouldn't.  An intermittent short to the A/B lines would also do the same.

Link to comment
Share on other sites

It would need to be a faulty device to be staying in write mode.  Depending on the Ethernet firmware, the level can dip down momentarily (buggy Honeywell firmware), so you can probably just ignore on the COM4 device and the virtual keypad for it KP15.

 

I think it's probably easier for you to swap devices until you have them all done. If this was at a customer site, I would say to just swap them all and then test them back in the office. It may be better doing the same at home in order to keep false alarms at a minimum.

 

Apart from that, you'd need to connect a bus analyser/recorder and watch the traffic in order to debug the issue.

Link to comment
Share on other sites

  • 2 weeks later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.

×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.