SIMONADT Posted August 31, 2008 Share Posted August 31, 2008 Dudes Had a callout to a series 3000 and the call engineer light was flashing with no fault on the display. got it into engineers, checked the fuses, power, battery etc etc, 99'd it but still it says call engineer. any ideas? had the same in the past but it came up with either a zone or a specific fault. si Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
camerabloke Posted August 31, 2008 Share Posted August 31, 2008 too old, bin it and stick a galaxy in Eucam Security Systems 0845 4630 746 www.eucam.co.uk Link to comment Share on other sites More sharing options...
SIMONADT Posted August 31, 2008 Author Share Posted August 31, 2008 customer wont pay... even on a service day works Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
abbz Posted August 31, 2008 Share Posted August 31, 2008 Check to see whether any of the ccts are on test. The call eng light flashes if the cct has failed Link to comment Share on other sites More sharing options...
SIMONADT Posted August 31, 2008 Author Share Posted August 31, 2008 Check to see whether any of the ccts are on test. The call eng light flashes if the cct has failed The last time someone was there was Feb this year for an RI... nothing is on test. Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
james.wilson Posted August 31, 2008 Share Posted August 31, 2008 whats in the log? securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment Share on other sites More sharing options...
abbz Posted August 31, 2008 Share Posted August 31, 2008 The last time someone was there was Feb this year for an RI... nothing is on test. Unlike modern day panels when you put a cct on test on a 9100 they stayed on test until they were removed via the programming and not after a certain amount of days. Ccts on test will still show up as normal on a walk test. Link to comment Share on other sites More sharing options...
SIMONADT Posted August 31, 2008 Author Share Posted August 31, 2008 Unlike modern day panels when you put a cct on test on a 9100 they stayed on test until they were removed via the programming and not after a certain amount of days. Ccts on test will still show up as normal on a walk test. nice one, i'll try that tomorrow then. The log doesnt work, it beeps to say end of list all the time!!! Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
breff Posted August 31, 2008 Share Posted August 31, 2008 Doesn't the 9100 do that on a panel lid tamper? try 99 with the tamper spring held down, those lids can be buggers to get on. The opinions I express are mine and are usually correct! (Except when I'm wrong)(which I'm not) Link to comment Share on other sites More sharing options...
SIMONADT Posted August 31, 2008 Author Share Posted August 31, 2008 Doesn't the 9100 do that on a panel lid tamper?try 99 with the tamper spring held down, those lids can be buggers to get on. it seemed to be locating the tamper when closing it but will try that too!!! can the lid t be linked out like Galaxy? Is the spring on a circuit with points anywhere? Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
Guest anguscanplay Posted August 31, 2008 Share Posted August 31, 2008 the beeping - log or "scroll " button? just follow these simple steps - engineer mode - zone number - three - should be 0 if its 1 thats on soak test - sack the other engineer - dont tell the customer - sorted Link to comment Share on other sites More sharing options...
SIMONADT Posted August 31, 2008 Author Share Posted August 31, 2008 the beeping - log or "scroll " button?just follow these simple steps - engineer mode - zone number - three - should be 0 if its 1 thats on soak test - sack the other engineer - dont tell the customer - sorted quality!!! consider him sacked. anyone for a job in the isle of man? lol Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
Guest anguscanplay Posted August 31, 2008 Share Posted August 31, 2008 quality!!!consider him sacked. anyone for a job in the isle of man? lol Ive seen sites where soak test was used to disconnect stuff, because your going to down the stu at half past bedtime so you can get to the terminals? yeah right lol Link to comment Share on other sites More sharing options...
hpotter Posted August 31, 2008 Share Posted August 31, 2008 Also, there was a quirky thing on 9100 where sometimes to clear "call eng" you had to go in and out (inc open lid tamp) twice to clear it. Link to comment Share on other sites More sharing options...
Guest anguscanplay Posted August 31, 2008 Share Posted August 31, 2008 Also, there was a quirky thing on 9100 where sometimes to clear "call eng" you had to go in and out (inc open lid tamp) twice to clear it. now that I`ve never come across, do remember that the customer couldnt reset tamper "H" activations though (mainly remembered because we connected the first couple of remote reset units to it - DOH) Link to comment Share on other sites More sharing options...
SIMONADT Posted August 31, 2008 Author Share Posted August 31, 2008 d'oh!! Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
hpotter Posted September 1, 2008 Share Posted September 1, 2008 Also, there was a quirky thing on 9100 where sometimes to clear "call eng" you had to go in and out (inc open lid tamp) twice to clear it. Similar problem, sometimes when you come out of eng zone 4 lit up for no reason. In & out of engineers clears it! Dont know why. Link to comment Share on other sites More sharing options...
Nova-Security Posted September 1, 2008 Share Posted September 1, 2008 can the lid t be linked out like Galaxy? Class..........Then the system wont conform. www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment Share on other sites More sharing options...
SIMONADT Posted September 1, 2008 Author Share Posted September 1, 2008 Class..........Then the system wont conform. sorry captain british standard!! Fire and Security Service Engineer ***Any views or statements above are not the views of my Employer*** Link to comment Share on other sites More sharing options...
Nova-Security Posted September 1, 2008 Share Posted September 1, 2008 sorry captain british standard!! Suppose you could link it out, then they get robbed and the loss adjuster finds panel lid link out, insureres wont pay out as system has one little deveation goes back to your compnay who finds out you where the last engineer on site pins blame on you, gets rid for gross misconduct shows up on your vetting cant get another job. As the saying goes 'if in doubt link it out' www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment Share on other sites More sharing options...
Guest anguscanplay Posted September 1, 2008 Share Posted September 1, 2008 Suppose you could link it out, then they get robbed and the loss adjuster finds panel lid link out, insureres wont pay out as system has one little deveation goes back to your compnay who finds out you where the last engineer on site pins blame on you, gets rid for gross misconduct shows up on your vetting cant get another job.As the saying goes 'if in doubt link it out' no doubt, but thats not what were discussing here Link to comment Share on other sites More sharing options...
lawandorder Posted September 1, 2008 Share Posted September 1, 2008 Suppose you could link it out, then they get robbed and the loss adjuster finds panel lid link out, insureres wont pay out as system has one little deveation goes back to your compnay who finds out you where the last engineer on site pins blame on you, gets rid for gross misconduct shows up on your vetting cant get another job.As the saying goes 'if in doubt link it out' How are you ever going to get back into engineer mode if you short the A/T? Link to comment Share on other sites More sharing options...
Guest anguscanplay Posted September 1, 2008 Share Posted September 1, 2008 How are you ever going to get back into engineer mode if you short the A/T? he isnt - someone mislead him that "call engineer" could be the lid tamper open (it isnt, an open tamper just bleeps and does nothing) ....... Link to comment Share on other sites More sharing options...
lawandorder Posted September 1, 2008 Share Posted September 1, 2008 How are you ever going to get back into engineer mode if you short the A/T? Yes I think you're right Angus, as I recall you cannot exit engineer mode with a lid tamper. I'm sure I have come across this problem with a 9100 before (call engineer flashing) but can't for the life the life of me remeber what it indicates. Is it the Auxillary zone open when trying to exit engineer mode or am I talking b******? Link to comment Share on other sites More sharing options...
Guest anguscanplay Posted September 1, 2008 Share Posted September 1, 2008 Yes I think you're right Angus, as I recall you cannot exit engineer mode with a lid tamper.I'm sure I have come across this problem with a 9100 before (call engineer flashing) but can't for the life the life of me remeber what it indicates. Is it the Auxillary zone open when trying to exit engineer mode or am I talking b******? cannot exit engineer mode with any tamper if your in engineer mode it means something on soak test flashes call engineer for tampers. line faults etc in customer mode Link to comment Share on other sites More sharing options...